Charge Pump (or Watchdog?) turns off when idle

More
01 Jan 2018 22:21 - 01 Jan 2018 22:31 #103937 by brianbonedoc
So this is a new one. I recently upgraded from PathPilot 1.9 to 2.0 which is linuxcnc 2.8 I believe.

Everything seems to be working fine, but if I leave my mill for a while, the charge pump turns off, and I have to restart pathpilot to reactivate it. Previously in 1.9 the charge pump would stay active indefinitely.

BTW - using 5i25 mesa board, w/ a Novakon Breakout board. And the firmware only has stepgen's so I am using stepgen to drive the charge pump.

The relevant watchdog and charge pump code is here:


# 5i25 watchdog timeout
# 10 milliseconds (~10 times the servo loop period)

setp hm2_[HOSTMOT2](BOARD).0.watchdog.timeout_ns 10000000

# Charge pump
# pin set by 5i25 configuration
# P3 pin 17 gpio 007
# ---Chargepump StepGen: 0.25 velocity = 10Khz square wave output---

setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.dirsetup 100
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.dirhold 100
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.steplen 50000
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.stepspace 500
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.position-scale 1
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.step_type 0
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.control-type 1
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.maxaccel 0
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.maxvel 11000
setp hm2_[HOSTMOT2](BOARD).0.stepgen.06.velocity-cmd 10000

Thanks in advance.
Last edit: 01 Jan 2018 22:31 by brianbonedoc.

Please Log in or Create an account to join the conversation.

More
02 Jan 2018 00:35 #103940 by PCW
It may be that the screensaver or some other function on your PC cause latency greater
than the 10 ms watchdog timeout period when idle for a long time

I would disable any power saving features that slow/halt the CPU when idle
You could also increase the WD timeout as a diagnostic

Please Log in or Create an account to join the conversation.

More
02 Jan 2018 00:48 #103941 by brianbonedoc
Thanks Peter! I just poked around to see if there were any power saving features, but it looks like everything is natively off in that regard.

I increased the watchdog timeout as you suggested, to 500 ms which is 50x longer than before. We'll see what happens.