07 Jun 2020 03:05 - 07 Jun 2020 03:05 #170435 by Mayberry Customs
E Stop Wiring was created by Mayberry Customs
I have wired the Mesa 7i76e all up but have just a quick question about my E stop...do I wire the E stop normally open or normally closed? I read a couple post about using the NO side wired to the input of the board which would trigger in software and then using the NC side to break one of the 24v field power wires to kill power to the board. Is this correct? Is there a configuration parameter that specifies NO or NC when wired to the input? Thanks, Andy
Last edit: 07 Jun 2020 03:05 by Mayberry Customs.

Please Log in or Create an account to join the conversation.

More
07 Jun 2020 07:26 #170439 by bbsr_5a
Replied by bbsr_5a on topic E Stop Wiring
NC is the safer way to do it
but it is up to you to do it as you like
if you are the only one user of the machine it does not matter

Please Log in or Create an account to join the conversation.

More
07 Jun 2020 08:49 #170447 by rodw
Replied by rodw on topic E Stop Wiring
If you hard wire your switch to drop AC Power to the motor power supply when pushed and then send +24v back to a 7i76e input to tell Linuxcnc estop has happened. Most estop switch are set up to allow this (NC one side, NO the other).
Each input has a matching -not pin in linuxcnc.

Please Log in or Create an account to join the conversation.

  • Mayberry Customs
  • Offline
  • Senior Member
  • Senior Member
More
07 Jun 2020 15:52 #170500 by Mayberry Customs
Replied by Mayberry Customs on topic E Stop Wiring
Ok great, thanks guys

Please Log in or Create an account to join the conversation.

More
07 Jun 2020 16:45 #170503 by Henk
Replied by Henk on topic E Stop Wiring
I pondered this some time ago when I completed my last retrofit.

This machine used the encoder output from the Chinese AC servo drive as feedback.

When you use the EStop to cut power to the drive, you lose encoder feedback. This can cause errors of a couple of counts everytime you hit the EStop. If you slam the EStop during motion, it is significant and you have to re-home.

Any ideas on the safest method in this case?


Also, cutting 24v power to the Mesa board is not good AFAIK.

Henk

Please Log in or Create an account to join the conversation.

  • tommylight
  • tommylight's Avatar
  • Away
  • Moderator
  • Moderator
More
07 Jun 2020 16:55 #170505 by tommylight
Replied by tommylight on topic E Stop Wiring
Older servo drives had always two power lines, the main one as a single or three phase, and another single phase for control power. In that case the main power can be disconnected at will and the position with persist.
New drives do not have that, so the only option is to use "enable" or in some cases they do have one or more "STO' pins, or safety turn off, so that would be used for e-stop.
The following user(s) said Thank You: Henk