Wiring - 24v field and 36v stepper drivers
- cadpete
- Offline
- Junior Member
Less
More
- Posts: 24
- Thank you received: 4
02 Oct 2022 01:11 #253213
by cadpete
Wiring - 24v field and 36v stepper drivers was created by cadpete
Sorry folks,
just having a brain fart moment.
I assume I have to tie the field power ground to the stepper motor ground for the signals to work. Logic says yes but tieing high and low current systems together seems a little counter intuitive.
Tia. Pete
just having a brain fart moment.
I assume I have to tie the field power ground to the stepper motor ground for the signals to work. Logic says yes but tieing high and low current systems together seems a little counter intuitive.
Tia. Pete
Please Log in or Create an account to join the conversation.
- arvidb
- Offline
- Platinum Member
Less
More
- Posts: 512
- Thank you received: 158
02 Oct 2022 11:48 #253245
by arvidb
Replied by arvidb on topic Wiring - 24v field and 36v stepper drivers
It depends entirely upon the specifics of your system. If your drives have opto-isolated IO then you don't have to connect the grounds (and probably shouldn't).
The following user(s) said Thank You: cadpete
Please Log in or Create an account to join the conversation.
- cadpete
- Offline
- Junior Member
Less
More
- Posts: 24
- Thank you received: 4
02 Oct 2022 14:23 #253253
by cadpete
Replied by cadpete on topic Wiring - 24v field and 36v stepper drivers
Linked grounds but the real problem was the drivers set for 24v signals but the Mesa giving only 5v even when on 24v field power.
X and Y motors now working but Z not responding.
X and Y motors now working but Z not responding.
Please Log in or Create an account to join the conversation.
- PCW
- Offline
- Moderator
Less
More
- Posts: 17950
- Thank you received: 4817
02 Oct 2022 15:00 - 02 Oct 2022 15:01 #253256
by PCW
Replied by PCW on topic Wiring - 24v field and 36v stepper drivers
The field I/O on Mesa cards is not related or connected to the step/dir interfaces
Mesa cards have 5V step/dir signals so the motor drives needs
to be set to accept 5V signals.
If you have a drive that does not work, the first suggestion is to
double the step time (don't use the minimum specified time)
Mesa cards have 5V step/dir signals so the motor drives needs
to be set to accept 5V signals.
If you have a drive that does not work, the first suggestion is to
double the step time (don't use the minimum specified time)
Last edit: 02 Oct 2022 15:01 by PCW.
Please Log in or Create an account to join the conversation.
- cadpete
- Offline
- Junior Member
Less
More
- Posts: 24
- Thank you received: 4
02 Oct 2022 22:01 #253291
by cadpete
Replied by cadpete on topic Wiring - 24v field and 36v stepper drivers
Thanks for the clarification.
All three motors and drivers (CL57T) are supposedly the same so I added 10 percent to the minimums for less error prone use.
The only exception is that the z drive is a V3 not v4 like the X and Y. This means that the set up is done by rs232 not just switches.
I have contacted the manufacturers as even bypassing my own wiring I am still getting encoder wiring error so I am starting to suspect a bad driver.
All three motors and drivers (CL57T) are supposedly the same so I added 10 percent to the minimums for less error prone use.
The only exception is that the z drive is a V3 not v4 like the X and Y. This means that the set up is done by rs232 not just switches.
I have contacted the manufacturers as even bypassing my own wiring I am still getting encoder wiring error so I am starting to suspect a bad driver.