What would be best practice to wire my 12V fans and pump to automatically start when the spindle is enabled?
I am aware of the PD050 setting to number 1 which is a out of the box setting.
Do I need to use a 24V relay or will the 7i76E handle 12V ?
Thanks.
Please Log in or Create an account to join the conversation.
- tommylight
- Away
- Moderator
- Posts: 19219
- Thank you received: 6440
Please Log in or Create an account to join the conversation.
- gardenweazel
- Topic Author
- Offline
- Premium Member
- Posts: 154
- Thank you received: 7
Please Log in or Create an account to join the conversation.
- tommylight
- Away
- Moderator
- Posts: 19219
- Thank you received: 6440
Or, if using a really small relay, adding a resistor in series with the coil is still manageable for 12V relay.
Please Log in or Create an account to join the conversation.
- gardenweazel
- Topic Author
- Offline
- Premium Member
- Posts: 154
- Thank you received: 7
Or even better what if I were to use something like this: www.amazon.com/Converter-DROK-Adjustable...ormer/dp/B08RBN31DT/
Connect it to the inverter 24v and use the built in inverter relay to switch on my water pump?
Please Log in or Create an account to join the conversation.
- tommylight
- Away
- Moderator
- Posts: 19219
- Thank you received: 6440
No idea if HY can do that, installed one of those once a few years back, but never checked if it can do that.
Connect it to the inverter 24v and use the built in inverter relay to switch on my water pump?
Some can by using the "at speed" output on the VFD so no need to wire anything to Mesa at all.
Please Log in or Create an account to join the conversation.
- warwickben
- Offline
- Junior Member
- Posts: 37
- Thank you received: 1
Please Log in or Create an account to join the conversation.
You can use LCNC's timing function(s) to let the pump run for a set period of time after the spindle is stopped. My spindle fan is set in HAL to turn on after 30 seconds of operation and stay on 2 minutes after the spindle is shut down. The 30 seconds is to stop the fan coming on during quickie testing or if it's just orienting for a tool change.
Have a look at timedelay.comp in the manual. You can connect spindle.N.on (see motion comp) to timedelay.N.in and timedelay.N.out to the water pump.
Please Log in or Create an account to join the conversation.
- itsgudenuf
- Offline
- New Member
- Posts: 7
- Thank you received: 2
I can't quite wrap my head on it all. I seem to be missing something.
Please Log in or Create an account to join the conversation.
You can trigger the time-delay signal from whatever you'd like. Signal SPINDLE-ENABLE is used to trigger both the time-delay as well as 7i76.0.0.spinena (physical spindle output pin).
In my case signal SPINDLE-ENABLE is triggered from an or2 component (due to a spindle orient setup), but spindle.0.on would be the logical pin to trigger the fan and actual spindle output.
As stated in the manual, on-delay is the time the timedelay.N.in signal must be on before the output goes high. If the spindle is only on for 20 seconds, the time-delay won't turn on in the below example. When the time delay input turns off, the off-delay setting keeps the output high until the off-delay time runs down.
If you are using spindle.N.fwd and/or spindle.N.rev instead of spindleN.on to command the spindle, then an or2 component can be used to trigger the time-delay input. Would look something like this:#SPINDLE FAN
setp timedelay.1.on-delay 30
setp timedelay.1.off-delay 120
net SPINDLE-ENABLE => [HMOT](CARD0).7i76.0.0.spinena
net SPINDLE-ENABLE => timedelay.1.in
net SPINDLE-FAN <= timedelay.1.out
net SPINDLE-FAN => [HMOT](CARD0).7i76.0.0.output-05
#SPINDLE FAN
setp timedelay.1.on-delay 30
setp timedelay.1.off-delay 120
net SPINDLE-FWD <= spindle.0.forward
net SPINDLE-FWD => or2.N.in0
net SPINDLE-REV <= spindle.0.reverse
net SPINDLE-REV => or2.N.in1
net SPINDLE-ON <= or2.N.out
net SPINDLE-ON => timedelay.1.in
net SPINDLE-FAN <= timedelay.1.out
net SPINDLE-FAN => [HMOT](CARD0).7i76.0.0.output-05