I've made a lot of progress on my Tree 325 retrofit using a 7i95T and 7i83. Digital inputs and outputs are working fine, and I can enable the analog outputs on the 7i83. When I start up the machine by pushing the "Power on machine" button in the GUI, the analog outputs enable, and all 3 axes of the machine move until one axis hits the MIN_FERROR limit, at which time I get a joint following error.
I've tried changing the scale signs to see if the problem was a direction mismatch. Changing the ENCODER_SCALE sign results in a swap in direction on the DRO, which is as expected. Changing the OUTPUT_SCALE sign has no effect...The machine always moves in the same direction.
I did a bit more troubleshooting on an unused analog output on the 7i83. With the analog output disabled, I read 0.001 V on my DMM. With the axis enabled using HalShow, I read .387 V while HalShow shows 0 for the output value. Changing the output value in HalShow results in no change to the output, which continues to read .387 V until the output is disabled.
All outputs appear to have this voltage offset when enabled, which explains the machine motion at startup and the joint following errors. Any ideas on what to try next?
I'm running 7i95 default firmware, and have not flashed anything to the 7i83 (remains as-delivered).
hal and ini files attached. They are still a bit of a work in progress.
Thanks,
Casey
Thanks,
Casey
Last edit: 15 Dec 2023 16:44 by cofford.
- Thank you received: 5308
15 Dec 2023 17:10 #288238
Replied by PCW on topic Voltage on 7i83 outputs
Are you saying that:
hm2_7i95.0.7i83.0.0.analogout0
is 0 but the output voltage is 0.387V?
If so there is a problem with the 7I83, and it should be returned to
Mesa for analysis/repair/replacement
- Thank you received: 7461
15 Dec 2023 17:50 #288243
Replied by tommylight on topic Voltage on 7i83 outputs
In the meantime, have a run through this, the "wiring and tuning" part, do some tests to see if the output react to changes in feedback.
15 Dec 2023 17:53 #288244
I should add that you should check the unused output with the other outputs unconnected
as a wiring error could cause a bad output level issue.
- cofford
15 Dec 2023 18:01 - 15 Dec 2023 18:03 #288245
by cofford
Replied by cofford on topic Voltage on 7i83 outputs
Darn it. That's exactly what's going on. The only connections I've made to the card are 24v+, gnd, and the analog out connections (and the serial RJ45). Is there any test I can do beforehand to make sure it needs to go back?
EDIT: just saw your reply. Will do, thanks.
Thanks,
Casey
Thanks,
Casey
Last edit: 15 Dec 2023 18:03 by cofford.
15 Dec 2023 18:07 #288250
Are you saying that you disconnected all the machine
drive wiring and you still get the 0.387V offset voltage?
- cofford
15 Dec 2023 18:10 #288251
by cofford
No, that's the one thing I haven't tried yet. Will do and will report back.
- cofford
15 Dec 2023 18:22 #288254
by cofford
FFS. I was measuring voltage on the enable pair instead of the analog out pair. All is well. Thanks for the help!
Time to create page: 0.647 seconds