Setting up 5i25+7i85+8i20
8 years 7 months ago #107868 by blazini36
Replied by blazini36 on topic Setting up 5i25+7i85+8i20
I didn't think quadrature would work since the hall sensors are not at 90 degrees.
By smoothing, do you mean something like the lowpass filter?
I assume Ill want to dump this into the motion controller, " => motion.spindle−speed−in"?
8 years 7 months ago #107870 by andypugh
Replied by andypugh on topic Setting up 5i25+7i85+8i20
Yes, I meant lowpass. And each pair of halls does a sort-of quadrature, enough to determine direction. They just have uneven timing so a velocity based on them will be noisy.
You don't actually need to send the velocity to motion on a milling machine. The point of having it is to use it with a PID component to get closed-loop velocity control.
8 years 7 months ago #108213 by blazini36
Using the hall sensors with the encoder component for a velocity feedback seems to work well. I would expect to see 16 counts from the 2 hall sensors in x4 mode but I see 12 per revolution so I have the encoder scale at 12. Lowpass gain of .01 seems to give a smooth velocity.
I am having alot of trouble with the PID loop. I can get it decent when the max output is limited to 2(amps), when I raise it to 7 I can't get the speed to come down. One thing I read suggests when tuning the PID, you should set I and D to 0 and raise P until the output oscillates, then I until the oscillation stops. I assume by "oscillate" it means starts making minor corrections when it's at speed. and not swinging between positive and negative values.
I seen PCW mention in another post that I and D should be left at 0 until it's close and only use P and FF0 until then, I have not tried this yet. I'm pretty sure I had to backdown on P because the motor would bang back and forth between hall counts when stopped. Looking at the docs, it says " the deadband should be set slightly more than one-half count". Does this actually mean .5 which is 1/2 of 1 count, or 6 which is 1/2 of counts per rev?
8 years 7 months ago #108215 by PCW
Replied by PCW on topic Setting up 5i25+7i85+8i20
For a spindle where the PID command is velocity and the PID output is torque,
you mainly want P and I
FF0 makes sense if the PID input and output are velocity but that's not the case with a torque mode drive.
Tuning a velocity loop is going to be tough with such poor (hall effect only) feedback, unless the spindle inertia
is quite high relative to the torque
8 years 7 months ago #108220 by andypugh
And for a spindle I would expect to be using I more than P. (The output of the P-term is zero when at the setpoint, but clearly 0 Amps won't give you a steady speed. Whereas it does give you a fixed position in a position loop)
8 years 7 months ago #108221 by blazini36
PCW wrote: For a spindle where the PID command is velocity and the PID output is torque,
Would it be better to use the spindles drilled disk for feedback than the hall sensors on the motor? It's a single photo interrupt sensor so no quadrature, and the disk only has 4 holes but theyre more consistently spaced than the 2/3 hall sensors. It'll be a bit before I get the parts to add the differential encoder to the motor so one of these will have to do for now.