Mesa 7i77 output scale
23 Jul 2013 00:27 #36895
by ROG
Mesa 7i77 output scale was created by ROG
I’ve gone back to basics with a meter on the analogue output of a Mesa 7i77
I’m struggling to work out the correct scale.
The manual mentions machine units per second.
With P/I/D etc set to zero and FF1 set to one, I’m getting some spurious readings on the output when MDIing a move at feeds of 110,220,1100 and 2200
Basically machine units are in mm
Rapid is 2220mm / min
Output should be +/-10v at 2200mm/ min = 36.66667 mm per/sec
So what should OUTPUT_SCALE = be set to?
MAX_OUTPUT = 10
OUTPUT_SCALE = -
OUTPUT_MIN_LIMIT = -10
OUTPUT_MAX_LIMIT = 10
MAX_OUTPUT = 10
OUTPUT_SCALE = -
23 Jul 2013 00:47 - 23 Jul 2013 01:09 #36896
Replied by PCW on topic Mesa 7i77 output scale
Those names are aliases but at some point the hal file needs to:
setp hm2_5i25.0.7i77.0.1.analogoutN.minlim -36.666
(probably OUTPUT_MIN_LIMIT)
setp hm2_5i25.0.7i77.0.1.analogoutN.maxlim 36.666
(probably OUTPUT_MAX_LIMIT)
setp hm2_5i25.0.7i77.0.1.analogoutN.scalemax 36.666
(probably OUTPUT_SCALE)
If you dont reset the min and max limit you will bound the output
to +- 10V/36.666
EDIT:
I forgot to say that you must have some headroom in the velocity command,
probably a minimum of 10% or so. If your drives are configured such that 10V
results in 2200 mm/m, I would not command a speed any faster than 2000 mm/min
so that the PID loop always has working room at the highest commanded speed
to +- 10V/36.666
EDIT:
Last edit: 23 Jul 2013 01:09 by PCW.
23 Jul 2013 01:03 #36899
by ROG
Replied by ROG on topic Mesa 7i77 output scale
Cheers Peter
setp hm2_5i25.0.7i77.0.1.analogout1-scalemax [AXIS_2]OUTPUT_SCALE (36.6666)
setp hm2_5i25.0.7i77.0.1.analogout1-minlim [AXIS_2]OUTPUT_MIN_LIMIT (36.6666)
setp hm2_5i25.0.7i77.0.1.analogout1-maxlim [AXIS_2]OUTPUT_MAX_LIMIT (36.6666)
mdi Z at FR of 1100mm/min = 2.7v with ff1 set to 1
what am I missing?
what am I missing?
23 Jul 2013 01:11 - 23 Jul 2013 01:16 #36901
I would trace the signals with halmeter
edit: 10/36.6 ~=2.7 so
Actually sounds like it being limited elsewhere, maybe PID maxoutput is set to 10?
Last edit: 23 Jul 2013 01:16 by PCW.
23 Jul 2013 01:19 #36902
by ROG
So theoretically, I should see 10V (ish) at a feed rate of 2200, 5V at 1100 and 1V at 220 if FF1 is set to 1 with all other PID values set to zero?
What about
setp pid.z.maxoutput [AXIS_2]MAX_OUTPUT
10 or 36.6666?
What about
10 or 36.6666?
23 Jul 2013 01:27 #36903
by ROG
pid.z.maxoutput [AXIS_2]MAX_OUTPUT ((36.6666))
FR2200 5.5V
Fr1100 5.5V
FR 220 1.5V
FR2200 5.5V
Fr1100 5.5V
FR 220 1.5V
23 Jul 2013 01:30 #36904
As I said before I would trace the signals with halmeter,
especially the PID output
Note, not that its the cause of the output bounding, but minlimit must be -36.66666
23 Jul 2013 01:38 #36906
by ROG
pid.z.output = 20.16 @ FR of 2200 mm/min ???
23 Jul 2013 01:52 #36907
well 20.16/36.6666 ~= 5.5V so the 7I77 is doing as requested
Maybe your max velocity is limited somewhere else,
suggest looking at axis.N.joint-vel-cmd
23 Jul 2013 02:06 #36908
by ROG
I concur – something is limiting the max velocity.
The output is now proportional.
As far as tuning is concerned, should I be looking at pid error or axis f-error, they have very different values?
Time to create page: 0.123 seconds