7i76 limits question..

More
29 Mar 2019 21:08 #129926 by B_Casey
when the signal is not inverted the switches show joint 0 and joint one on limit switch error.
so i inverted the signals.. now the switches to not register at all.
have tested the switches with a meter, the switches are working
the e-stop is doing the same thing...

not sure what could be causing this issue, (the same switches and e-stops where functioning fine on the 5i25-g540 before i put the 7i76

12v field power
5v other power
both leds are on
field pwr ->switch -> input on 7i76

Brian

Please Log in or Create an account to join the conversation.

More
30 Mar 2019 14:54 #129971 by B_Casey
Replied by B_Casey on topic 7i76 limits question..
figured this out, it was a typo in the server period thing, was causing the sserial to shut down due to errors, (left off one of the zeros)

Please Log in or Create an account to join the conversation.

More
30 Mar 2019 22:10 #130000 by tommylight
Replied by tommylight on topic 7i76 limits question..
Thank you for reporting back.
Glad you got it working.
The following user(s) said Thank You: B_Casey

Please Log in or Create an account to join the conversation.

More
31 Mar 2019 02:30 #130010 by PCW
Replied by PCW on topic 7i76 limits question..
You should have gotten a cascade of error messages if you lost contact with the 7I76

If you want to generate a fault if you lose contact with a sserial remote, you can use the

hm2_(card).0.sserial.port-0.run

pin to monitor the health of sserial connections
The following user(s) said Thank You: B_Casey

Please Log in or Create an account to join the conversation.

More
31 Mar 2019 02:34 #130011 by B_Casey
Replied by B_Casey on topic 7i76 limits question..
there was and your response to someone else some other when clued me into what the problem was !