Huanyang VFD with 2,2 kw chinesium spindle
30 Jan 2020 11:21 #156160
by MovT
Huanyang VFD with 2,2 kw chinesium spindle was created by MovT
Hi.
I want to bring my chinesium spindle to work with help here. But i only have one speed at the spindle. I stuck now. No matter what speed i will set e.g. M3 S12000 the spindle will start and stop acceleration at 6000 rpm. M3 S0 stops the spindle. All work well but not the speed settings.
Here the config snippets:
LinuxCNC Version 2.8
Custom HAL
.ini
.hal
I would be very happy when i get it working as expected.
Thanks,
Udo
I want to bring my chinesium spindle to work with help here. But i only have one speed at the spindle. I stuck now. No matter what speed i will set e.g. M3 S12000 the spindle will start and stop acceleration at 6000 rpm. M3 S0 stops the spindle. All work well but not the speed settings.
Here the config snippets:
LinuxCNC Version 2.8
Custom HAL
loadusr -Wn vfd hy_vfd -n vfd -d /dev/ttyUSB0 -p none -r 9600
#loadusr -Wn vfd hy_vfd -n vfd -t 1 -d /dev/ttyUSB0 -p none -r 9600 -s 1 -S 24000 -F 400 -f 100 -V 220 -I 11 -P 4
net spindle-cmd-rpm-abs => vfd.speed-command
net spindle-cw spindle.0.forward => vfd.spindle-forward
net spindle-ccw spindle.0.reverse => vfd.spindle-reverse
net on spindle.0.on => vfd.spindle-on => hm2_7i76e.0.7i76.0.0.output-13
net spindle-at-speed => vfd.spindle-at-speed
setp vfd.enable 1
.ini
[SPINDLE_0]
P = 0
I = 0
D = 0
FF0 = 1
FF1 = 0
FF2 = 0
BIAS = 0
DEADBAND = 0
MAX_OUTPUT = 24000.0
OUTPUT_MIN_LIMIT = 6000
OUTPUT_MAX_LIMIT = 24000
OUTPUT_SCALE = 24000
.hal
#*******************
# SPINDLE
#*******************
setp pid.s.Pgain [SPINDLE_0]P
setp pid.s.Igain [SPINDLE_0]I
setp pid.s.Dgain [SPINDLE_0]D
setp pid.s.bias [SPINDLE_0]BIAS
setp pid.s.FF0 [SPINDLE_0]FF0
setp pid.s.FF1 [SPINDLE_0]FF1
setp pid.s.FF2 [SPINDLE_0]FF2
setp pid.s.deadband [SPINDLE_0]DEADBAND
setp pid.s.maxoutput [SPINDLE_0]MAX_OUTPUT
setp pid.s.error-previous-target true
net spindle-index-enable <=> pid.s.index-enable
net spindle-enable => pid.s.enable
net spindle-vel-cmd-rpm => pid.s.command
net spindle-vel-fb-rpm => pid.s.feedback
net spindle-output <= pid.s.output
# ---setup spindle control signals---
net spindle-vel-cmd-rps <= spindle.0.speed-out-rps
net spindle-vel-cmd-rps-abs <= spindle.0.speed-out-rps-abs
net spindle-vel-cmd-rpm <= spindle.0.speed-out
net spindle-vel-cmd-rpm-abs <= spindle.0.speed-out-abs
#net spindle-enable <= spindle.0.on
#net spindle-cw <= spindle.0.forward
#net spindle-ccw <= spindle.0.reverse
net spindle-brake <= spindle.0.brake
net spindle-revs => spindle.0.revs
net spindle-at-speed => spindle.0.at-speed
net spindle-vel-fb-rps => spindle.0.speed-in
net spindle-index-enable <=> spindle.0.index-enable
# ---Setup spindle at speed signals---
sets spindle-at-speed true
I would be very happy when i get it working as expected.
Thanks,
Udo
Please Log in or Create an account to join the conversation.
30 Jan 2020 11:38 #156163
by bbsr_5a
Replied by bbsr_5a on topic Huanyang VFD with 2,2 kw chinesium spindle
is the Parameter set to get speed from the RS485
the hyanjang also got a Jumper
seams you only set the start stop to the USB signal
the hyanjang also got a Jumper
seams you only set the start stop to the USB signal
Please Log in or Create an account to join the conversation.
30 Jan 2020 12:50 #156173
by MovT
Replied by MovT on topic Huanyang VFD with 2,2 kw chinesium spindle
Yes all works still under Windows 7 with Mach3 and the VFD driver. Same machine same wiring etc.
How i can debug the communication?
tail -f /dev/ttyUSB0 didnt work ;(
How i can debug the communication?
tail -f /dev/ttyUSB0 didnt work ;(
Please Log in or Create an account to join the conversation.
30 Jan 2020 14:55 #156183
by MovT
Replied by MovT on topic Huanyang VFD with 2,2 kw chinesium spindle
5 Minutes ago i go back to Mach3 and test the spindle. All works fine and the speed went up to 24000 rpm.
I can't figure out what i miss in my config.
by the way, the vfd.speed-comand is always 0. vfd.rott says 6000 rpm if th spindle run. Thats very weird.
Any help will be appreciated.
Best,
Udo
I can't figure out what i miss in my config.
by the way, the vfd.speed-comand is always 0. vfd.rott says 6000 rpm if th spindle run. Thats very weird.
Any help will be appreciated.
Best,
Udo
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
Less
More
- Posts: 5007
- Thank you received: 1441
30 Jan 2020 17:37 #156191
by Todd Zuercher
Replied by Todd Zuercher on topic Huanyang VFD with 2,2 kw chinesium spindle
Does your spindle have encoder feedback? If it doesn't why do you have a pid configured. The PID can't close the loop without feedback.
Please Log in or Create an account to join the conversation.
30 Jan 2020 19:30 #156197
by MaHa
Replied by MaHa on topic Huanyang VFD with 2,2 kw chinesium spindle
My configuration, another vfd but hf spindle and 7i76e. It's pncconf wizard generated and modified.
In the .ini file this entry.
the output scale was needed, to get 6000rpm at 100 Hz and 24000rpm at 400Hz.
In hal, timedelay for speedupdelay, and lincurve to set any s lower than 6000 to 6000 and limit to 24000rpm is also in my config.
In the .ini file this entry.
#********************
# Spindle
#********************
[SPINDLE_9]
P = 0.0
I = 0.0
D = 0.0
FF0 = 1.0
FF1 = 0.0
FF2 = 0.0
BIAS = 0.0
DEADBAND = 0.0
MAX_OUTPUT = 24000.0
OUTPUT_SCALE = 26000
OUTPUT_MIN_LIMIT = 0
OUTPUT_MAX_LIMIT = 24000
the output scale was needed, to get 6000rpm at 100 Hz and 24000rpm at 400Hz.
In hal, timedelay for speedupdelay, and lincurve to set any s lower than 6000 to 6000 and limit to 24000rpm is also in my config.
loadrt timedelay count=1
loadrt lincurve personality=4
addf timedelay.0 servo-thread
addf lincurve.0 servo-thread
setp timedelay.0.on-delay 4
setp timedelay.0.off-delay 0
#*******************
# SPINDLE S
#*******************
setp pid.s.Pgain [SPINDLE_9]P
setp pid.s.Igain [SPINDLE_9]I
setp pid.s.Dgain [SPINDLE_9]D
setp pid.s.bias [SPINDLE_9]BIAS
setp pid.s.FF0 [SPINDLE_9]FF0
setp pid.s.FF1 [SPINDLE_9]FF1
setp pid.s.FF2 [SPINDLE_9]FF2
setp pid.s.deadband [SPINDLE_9]DEADBAND
setp pid.s.maxoutput [SPINDLE_9]MAX_OUTPUT
setp pid.s.error-previous-target true
# ---auto rpm: 1-6000 = 6000 / 24000 max
setp lincurve.0.x-val-00 0
setp lincurve.0.y-val-00 0
setp lincurve.0.x-val-01 1
setp lincurve.0.y-val-01 6000
setp lincurve.0.x-val-02 6000
setp lincurve.0.y-val-02 6000
setp lincurve.0.x-val-03 24000
setp lincurve.0.y-val-03 24000
net spindle-index-enable <=> pid.s.index-enable
net spindle-enable => pid.s.enable
net spindle-vel-cmd-rpm-abs => pid.s.command
net spindle-vel-fb-rpm-abs => pid.s.feedback
net spindle-output <= pid.s.output
# ---digital potentionmeter output signals/setup---
setp hm2_7i76e.0.7i76.0.0.spinout-minlim [SPINDLE_9]OUTPUT_MIN_LIMIT
setp hm2_7i76e.0.7i76.0.0.spinout-maxlim [SPINDLE_9]OUTPUT_MAX_LIMIT
setp hm2_7i76e.0.7i76.0.0.spinout-scalemax [SPINDLE_9]OUTPUT_SCALE
net spindle-output => hm2_7i76e.0.7i76.0.0.spinout
net spindle-enable => hm2_7i76e.0.7i76.0.0.spinena timedelay.0.in
net spindle-cw => hm2_7i76e.0.7i76.0.0.spindir
# ---setup spindle control signals---
net spindle-vel-cmd-rps <= motion.spindle-speed-out-rps
net spindle-vel-cmd-rps-abs <= motion.spindle-speed-out-rps-abs
net spindle-vel-cmd-rpm <= motion.spindle-speed-out
net spindle-pre <= motion.spindle-speed-out-abs lincurve.0.in
net spindle-vel-cmd-rpm-abs <= lincurve.0.out
net spindle-enable <= motion.spindle-on
net spindle-cw <= motion.spindle-forward
net spindle-ccw <= motion.spindle-reverse
net spindle-brake <= motion.spindle-brake
net spindle-revs => motion.spindle-revs
net spindle-at-speed => motion.spindle-at-speed timedelay.0.out
net spindle-vel-fb-rps => motion.spindle-speed-in
net spindle-index-enable <=> motion.spindle-index-enable
# sets spindle-at-speed true
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
Less
More
- Posts: 5007
- Thank you received: 1441
30 Jan 2020 20:09 - 30 Jan 2020 20:10 #156200
by Todd Zuercher
Replied by Todd Zuercher on topic Huanyang VFD with 2,2 kw chinesium spindle
If he is simply commanding the VFD through modbus, (not the 7i76's analog out). There should be no reason to scale an output. Also the VFD can have its parameters set to honor the minimum and max speeds and ramp speed, so there would be no need for the Limit3. Simply connecting the motion. spindle-speed-out to hal pin for the serial driver.
It may be helpful if you posted your entire hal file rather than snippets of it.
At this point I'm not sure if the VFD is starting and being ran by physical connections to your 7i76 or by the serial connection. You seem to have both in your hal file. If you intend to run using the serial connections you should not connect the physical ones. On a lot of these drives if you enable the terminal strip inputs you must disable the serial link and vice versa.
It may be helpful if you posted your entire hal file rather than snippets of it.
At this point I'm not sure if the VFD is starting and being ran by physical connections to your 7i76 or by the serial connection. You seem to have both in your hal file. If you intend to run using the serial connections you should not connect the physical ones. On a lot of these drives if you enable the terminal strip inputs you must disable the serial link and vice versa.
Last edit: 30 Jan 2020 20:10 by Todd Zuercher.
Please Log in or Create an account to join the conversation.
30 Jan 2020 22:37 - 30 Jan 2020 22:39 #156211
by MovT
Replied by MovT on topic Huanyang VFD with 2,2 kw chinesium spindle
All answers sounds very cryptic. I am a beginner in LinuxCnC. My first attempt was in a case successful. The Spindle starts but the vfd.command-speed wasn't delivered by any kind of the examples.
I digged deeeper in the signal chain and grab the first input and so what - it works now.
The line:
net spindle-cmd-rpm-abs => vfd.speed-command
was changed to :
net spindle-vel-cmd-rpm => vfd.speed-command
and all was fine.
M3 S12000 bring the spindle to 12000 rpm and if the spindle achieved the target rpm spindle-at-sped will set to true.
Thanks anyway guys.
Hope the rest will be in the same manner.
Best,
Udo
I digged deeeper in the signal chain and grab the first input and so what - it works now.
The line:
net spindle-cmd-rpm-abs => vfd.speed-command
was changed to :
net spindle-vel-cmd-rpm => vfd.speed-command
and all was fine.
M3 S12000 bring the spindle to 12000 rpm and if the spindle achieved the target rpm spindle-at-sped will set to true.
Thanks anyway guys.
Hope the rest will be in the same manner.
Best,
Udo
Last edit: 30 Jan 2020 22:39 by MovT.