Modbus VFD startup delay?
- spumco
- Thank you received: 905
01 Sep 2024 02:10 #309122
by spumco
Modbus VFD startup delay? was created by spumco
Just for fun I thought I'd try to use modbus - specifically gs2_vfd - to control my mill spindle. VFD is a GS3 from Automation Direct, currently using 0-10v.
After some config problems (tty permissions), the USB-RS-485 adapter and LCNC are sort-of talking to the VFD.
I'm getting 'failed to set register - communication timed out' errors, but I think I have a more serious problem...
The way I've set up my electrical system, when estop is asserted, all the drives and VFD have no mains power. 24vdc is present for all sensors, Mesa, and so forth, but no drive bus power.
Until I de-assert estop, the VFD is dead and can't communicate with LCNC - so LCNC shuts down due to a 'no response' error. I got around that for testing by taking it out of estop and energizing the contactors (having bypassed some HAL safety logic) and then starting LCNC.
Which got me thinking... is there a way to delay LCNC trying to communicate with the VFD until after I de-assert estop?
I'm not willing to change my estop scheme to permit power to the VFD when estop is asserted. And the VFD has no separate logic power input like some servo drives.
Putting the 'loadusr Wn...' in the postgui file didn't do the trick. I don't take it out of estop until the GUI is up and stable.
There's no point in trying to troubleshoot the read/write unless I can force LCNC to wait until after I de-assert estop. Anyone have a thought on this?
- Thank you received: 2176
01 Sep 2024 14:51 #309154
Replied by Aciera on topic Modbus VFD startup delay?
There are probably ways to start the modbus component and the associated hal file through a custom Mcode but I don't see how you would be able to restart the modbus connection after an estop event.
It seems that this should really be handled in the modbus component itself.
- spumco
01 Sep 2024 21:15 #309170
by spumco
Replied by spumco on topic Modbus VFD startup delay?
Thanks. I'm not going down the component editing rabbit-hole, so I'll stick with the existing analog control.
- COFHAL
- Thank you received: 62
02 Sep 2024 01:20 #309179
by COFHAL
Replied by COFHAL on topic Modbus VFD startup delay?
I don't quite understand your problem. I control my VFD via MODBUS and when communication is lost an error message appears, but once communication is re-established everything returns to normal. The error you describe would only appear if at the start of LNC there was no communication with the VFD. If I disconnect the power supply to the VFD only the error message appears, but once I re-establish it everything returns to normal.
- COFHAL
02 Sep 2024 01:32 #309180
by COFHAL
Let me clarify, I am using the VFDMOD component with a USB to 485 converter and MESA MODBUS through the RS422 port of the MESA cards, and that error that you describe, that is, LCNC shuts down at startup only if there is no communication with the VFD when it is starting up. Once LCNC starts and if there are subsequently communication problems with the VFD, it only tells me that there is an error but does not shut down.
- spumco
02 Sep 2024 04:33 #309186
by spumco
@COFHAL-
Yes, because my VFD is not powered at startup, LCNC shuts down with a modbus error.
What I was asking earlier is if there is a way to delay LCNC trying to communicate with the VFD until after LCNC has finished starting up. Specifically, after estop is deasserted and machine-on is true.
Ideally, estop-clear would trigger LCNC to attempt communication with the VFD, and perhaps prohibit machine-on if communications weren't established after some time.
02 Sep 2024 06:53 #309194
So, once the startup procedure has successfully completed, does your component reconnect automatically after a powerloss in the VFD? If so then my comment above would not be accurate and the startup delay was really all that is needed.
- MennilTossFlykune
- Thank you received: 30
02 Sep 2024 07:09 #309195
by MennilTossFlykune
Replied by MennilTossFlykune on topic Modbus VFD startup delay?
what about the gs2_vfd enable pin?
02 Sep 2024 08:08 #309199
The 'gs2_vfd' component does not seem to have an 'enable' pin:
linuxcnc.org/docs/stable/html/man/man1/gs2_vfd.1.html
- MennilTossFlykune
02 Sep 2024 08:33 #309200
Time to create page: 1.142 seconds