I can't reverse the spindle rotation.
4 months 1 week ago - 4 months 1 week ago #347333 by PCW
The Isolator is doing 5V to 24V translation so unless the BOB has a relay/24V output
it cannot go directly to the VFD
Sounds like maybe  grounding issue (or damaged OPTO)
Note that a parallel port ground is nearly always frame ground
but the 7I92 ground may be floating
Last edit: 4 months 1 week ago by PCW.
4 months 1 week ago #347334 by tommylight
Sorry, i missed 5V/24V thing above.
I edited the above posts.
The following user(s) said Thank You: Ismacr63
4 months 1 week ago #347335 by tommylight
Now the question becomes:
will the servo drive work with 5V on the inputs?
Did you check the manual?
Older drives do not, but all new-ish ones do.
Now i wonder if i missed how old is your drive! :)
4 months 1 week ago #347336 by Ismacr63
The servomotor uses the ECAC XP200 driver, and according to the manual, the digital inputs can only be controlled with 24V.
I also have the ground for the 7i92 tied to the common ground.
4 months 6 days ago #347354 by Ismacr63
Alright, bit of progress. I did some testing and managed to get the PC817 module working — at least for now.
The module has a 302Ω resistor on both the input and output side. When the LED turned on, the output voltage only dropped to about 21V, so the servo driver wasn't seeing it as a proper low signal.
I tried putting another resistor in parallel with the one already on the output side, and bingo — reverse works. With a 3k resistor in parallel, the output drops to around 14V. With a 1.5k, it drops to about 10V. Both values make the servo reverse properly.
So my question now is, what's a safe resistor value to leave in there permanently? I don't want to damage anything, but I need it to work reliably. What would you guys recommend?
4 months 6 days ago - 4 months 6 days ago #347356 by PCW
Honestly it sounds like you should be using a Darlington OPTO in place
of the low CTR PC817, say a LTV-815 or similar.
( PC817 mas a minimum CTR of 50% vs the LTV-815's 600% minimum )
Last edit: 4 months 6 days ago by PCW. Reason: wrong PN
The following user(s) said Thank You: tommylight, Ismacr63
Time to create page: 0.120 seconds