Need help with unexpected/random stops on basic Parport/5 axis BOB setup
- tommylight
- Away
- Moderator
-
That is not good, but at least now you have a route to follow :Lezard wrote: - same, enabled : readings between 110 and 440Vac (!!), from a multimeter set to 500Vac scale
Check the breaker boxes for loose ground wires,
Check all the sockets/plugs en route to the machine for proper ground wiring,
Check if you have a ground fault interrupter, if you do not, install one immediately, that is a must, not an option.
Then you have to check the equipment and find what is causing all that potential to run to the ground.
BTW, do not touch the machine while powered on and enabled and wear good isolating shoes, ruining shoes do just fine.
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
- Posts: 4793
- Thank you received: 1480
That said, I am also having the exact same trouble with the same Chinese BOB. The input I am/was using for e-stop suddenly went intermittent. I've worked around it for now by connecting a 2nd unused input in parallel then to an or2 in hal. Mostly I think it is just a design defect or bad module on these cheap boards.
Please Log in or Create an account to join the conversation.
- Lezard
- Offline
- Senior Member
-
- Posts: 56
- Thank you received: 4
Todd Zuercher wrote: ... I've worked around it for now by connecting a 2nd unused input in parallel then to an or2 in hal. Mostly I think it is just a design defect or bad module on these cheap boards.
Thank you for your suggestion. I've done the same, it sort of improved things a bit, but I still had unexpected stops. I've read also about the debounce function, this might also help, haven't tried that yet. This cheap Bob was intended as a stepping stone towards a more robust solution, I stll plan to upgrade it as soon as cash allows...
tommylight wrote: Check the breaker boxes for loose ground wires,
Check all the sockets/plugs en route to the machine for proper ground wiring,
Check if you have a ground fault interrupter, if you do not, install one immediately, that is a must, not an option.
I appreciate your concern re. safety. I do have a 30mA ground fault interrupter installed at the main electrical panel in the workshop, if that is what you mean ( not sure about the correct translation here) It does work : I just triggered it when I inadvertently touched a phase wire with a ground connected wire... All parts of the machine are also connected (including gantry and Z-axis) and grounded at the CNC cabinet ground.
I've attached a thick copper wire from the CNC cabinet chassis, and pulled it near the electrical panel from where the CNC is wired. Resistance between the end of this cable and the GND on the electrical panel reads as 2 Ohms (control wire is 10mm diameter copper strand, +/-20m long). So I believe the cabinet is grounded, at least it's connected to the GND at the electrical panel.
Am I wrong ?
I have also pulled the same thick wire directly from the CNC cabinet chassis to the building ground stake, to bypass all the ground wiring : this has no effect on the ripples on the PC screen.
The friend who helped me with the wiring can"t join me, as we are under travel restrictions due to the COVID-19...
I'm a bit lost !
Please Log in or Create an account to join the conversation.
- tommylight
- Away
- Moderator
-
- Posts: 22011
- Thank you received: 7491
Had the same problem with a cheap BOB, the optocouplers would weaken with time and needed more current to open properly. Adding some resistors parallel to the existing ones on the inputs did remedy that and luckily had no issues with it anymore.
@ Lezard,
Yes, that is the GFI in US or FID here in Europe. To test it's functionality just short the ground to the neutral, they are both located at the bottom of the socket and open to access, here in Europe.
If i remember correctly, whenever i measured between two grounds in my shop, i always get less than 1 Ohm.
Please Log in or Create an account to join the conversation.
- Lezard
- Offline
- Senior Member
-
- Posts: 56
- Thank you received: 4
- the CNC cabinet GND _is_ connected to the building GND
- I may have un-expectedly high levels of EMI, some of these find their way to the PC, perturbating the PC screen and the reading of the inputs on the parport
- powering the PC from outside the CNC cabinet seems to alleviate the problem : no more ripples on the PC screen, and no more false readings of the e-stop
- EMI seem to come from the axis Delta vars : when I power only the spindle VFD, I see no ripples on the PC screen
Does this seem correct ?
When the PC is powered outside the cabinet, its GND connection is distinct (?) from the CNC GND. Is that why it seems to fix things ? If that were the case, this would mean that the perturbations come not from faulty isolation of the Bob, but rather from the common GND ?
@Todd : can you give some more details on how I could add an EMI before the vars ?
Thank you all for your help and time
Laurent
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
- Posts: 4793
- Thank you received: 1480
Here is a little reading.
support.automationdirect.com/docs/emi_mitigation.pdf
Please Log in or Create an account to join the conversation.