Yes, it consistently appears to be around 10ms.
However, I believe I’ve found a workaround. I have noticed, that the EL5101 outputs the encoder period which is an absolutely stable signal. So I wrote a custom component to calculate the frequency based on it, which in turn can be used in PlasmaC. In the attached Halscope screenshot, you can see the troublesome frequency signal with drops from the EL5101 in red, the encoder period in cyan, and the calculated frequency in green.
However, I believe I’ve found a workaround. I have noticed, that the EL5101 outputs the encoder period which is an absolutely stable signal. So I wrote a custom component to calculate the frequency based on it, which in turn can be used in PlasmaC. In the attached Halscope screenshot, you can see the troublesome frequency signal with drops from the EL5101 in red, the encoder period in cyan, and the calculated frequency in green.
loadrt period_to_freq names=period_to_freq-thc
addf period_to_freq-thc servo-thread
net measured-period-thc lcec.0.EL5101_THC.enc-period => period_to_freq-thc.period-in
net plasmac:arc-voltage-in <= period_to_freq-thc.frequency
Please Log in or Create an account to join the conversation.
- Hakan
- Away
- Platinum Member
-
Less
More
- Posts: 543
- Thank you received: 176
16 Feb 2025 05:27 #321682
by Hakan
Replied by Hakan on topic THC with Beckhoff EL5101 and THCAD2 => encoder signal loss
I looked through the EL5101 docs and - did I get it right? - it measures frequency by counting number of edge rises during a 10 ms window? Could be where 10 ms comes from. Seems low resolution also, frequency will be in steps of 100 Hz.
The following user(s) said Thank You: rodw
Please Log in or Create an account to join the conversation.
- Sandro
- Offline
- Senior Member
-
Less
More
- Posts: 50
- Thank you received: 13
16 Feb 2025 09:31 - 16 Feb 2025 12:32 #321693
by Sandro
Replied by Sandro on topic THC with Beckhoff EL5101 and THCAD2 => encoder signal loss
Yes, indeed. However since the drops seem to be random, I am not sure if it is related.
The manual also states that no frequency measurement is possible if the counter is blocked by the gate, but that in this case the period can be measured regardless.
And further: If an encoder signal is only present at input A/A and the frequency/period is to be measured, the terminal must be set to “Enable FWD count” in CoE 0x8000:03 [} 155].
The manual also states that no frequency measurement is possible if the counter is blocked by the gate, but that in this case the period can be measured regardless.
And further: If an encoder signal is only present at input A/A and the frequency/period is to be measured, the terminal must be set to “Enable FWD count” in CoE 0x8000:03 [} 155].
Attachments:
Last edit: 16 Feb 2025 12:32 by Sandro.
Please Log in or Create an account to join the conversation.
- Hakan
- Away
- Platinum Member
-
Less
More
- Posts: 543
- Thank you received: 176
16 Feb 2025 10:16 #321709
by Hakan
Replied by Hakan on topic THC with Beckhoff EL5101 and THCAD2 => encoder signal loss
If the pulse length method works for you it is even better. 100 ns resolution between two rising edges gives 0.1 Hz resolution and seems to be updated every cycle.
Please Log in or Create an account to join the conversation.
- rodw
-
- Away
- Platinum Member
-
Less
More
- Posts: 10965
- Thank you received: 3642
16 Feb 2025 10:58 #321712
by rodw
Replied by rodw on topic THC with Beckhoff EL5101 and THCAD2 => encoder signal loss
I had a quick look at the manual and I saw something that indicated the drop to zero was an index mark. My guess is that one of the PDOs needs to be set to remove it.
As I said earlier in the Ethercat world, a 0-10 volt analog input is probably a better choice but I have not tried one (assuming the plasma cutter has a voltage divider).. The EL3061 for example offers 500 volt isolation which is similar to the Mesa THCAD. To scale the voltage you would just need to use a mult2 component, send the output to QTplasmac and set the Qtplasmac offset to zero and the scale to 1.
As I said earlier in the Ethercat world, a 0-10 volt analog input is probably a better choice but I have not tried one (assuming the plasma cutter has a voltage divider).. The EL3061 for example offers 500 volt isolation which is similar to the Mesa THCAD. To scale the voltage you would just need to use a mult2 component, send the output to QTplasmac and set the Qtplasmac offset to zero and the scale to 1.
Please Log in or Create an account to join the conversation.
- Hakan
- Away
- Platinum Member
-
Less
More
- Posts: 543
- Thank you received: 176
17 Feb 2025 06:05 #321800
by Hakan
Replied by Hakan on topic THC with Beckhoff EL5101 and THCAD2 => encoder signal loss
I think one can not take for granted that EL3061's signal ground is the same potential as the workpiece ground. If you are lucky it might work, but to be on the safe side the torch signals should be isolated and free to float.