Configuring LinuxCNC
Advanced Configuration
Servo Tuning Advice
Servo Tuning Advice
Thank you received: 4359
01 Oct 2012 17:13 - 01 Oct 2012 17:22 #24821
For a torque loop I would add P and D until it cannot be made stable
(more D will allow more P up to a point) then back off on both proportionally until its stable again. (do this with no I term)
Then as I said before, add I until its unstable and then use 1/2 to 1/3 of that amount of I
I suspect you need 10 to 1000 times more I
Last edit: 01 Oct 2012 17:22 by
PCW.
Thank you received: 1370
01 Oct 2012 17:21 #24822
PCW wrote:
Yes, heres a static error (250 uInch) in the middle that the Integral term should pull in
I would make the integral term larger until it gets unstable and then use about 1/2 to 1/3 of that amount. Seems like the deadband could be smaller as well just so it does not interfere with interpretation of the plots
When I make "I" large the whole thing starts shifting up (like adding more bias). Is it normal for this to happen? Then should I use the bias to pull it back to 0?
01 Oct 2012 17:27 - 01 Oct 2012 17:42 #24823
No that makes no sense. Something is wrong if 'I' term behaves this way. it should at the least start to pull in the static error to 0
A plot would help
Last edit: 01 Oct 2012 17:42 by
PCW.
01 Oct 2012 18:31 #24825
But most of the tuning threads on the forum that I've looked at said that a lot of I was bad.
After about 5000 or so I stopped moving the error away like the bias, and started to bring the steady state error in line.
01 Oct 2012 19:22 #24830
You _may_ be able to reduce the width of the error spikes at the
beginning and ending of motion by increasing 'I' further
03 Oct 2012 13:50 #24906
I am a bit frustrated again. Made some different length moves at different speeds and the steady state error came back with a vengence. I am not sure where the solution lies. But right now I'm to buisy with other things to mess with it.
30 Oct 2012 19:33 #26055
I've finally had a little time to play with it again. I was not able to able to add enough I to cause instability. However having an I of 50K did result in a very interestingly odd shaped f-error plots in hal-scope. I'll post a pictuer of it later. Also I don't understand why adding "I" is messing with the bias number so much.
Thank you received: 4803
30 Oct 2012 19:50 #26056
"I-term windup" may be the problem. The I term increases all the time there is an error, then a small overshoot causes it to reduce again, but very slowly.
Some controllers zero out the I term when the error term changes sign. (But sometimes that is very much the wrong thing to do)
30 Oct 2012 23:09 #26076
Are there any simple tricks to make the ouput scale positive? I wonder if I have a positive/negative problem screwing with the PID math. I ran it backwards a little the other day and I thought things seemed a little better, so I switched 2 encoder wires to reverse that, but I haven't found a simple way to reverse the motor, (I don't want to deal with swiching a power wire and re figuring out the hall sensors (that was much to painful the last time). I will have a look at the drive software I might be able to do it there. I know it can for step/dir, but I don't know about analog torque mode.
Servo Tuning Advice
Time to create page: 1.020 seconds