-no grounding
-bad/looped grounding
-bad/weak power supply
-error in wiring
-EMI/interference from drives/VFD
-PC with no ground connection
In that order, mostly.
-bad/looped grounding
-bad/weak power supply
-error in wiring
-EMI/interference from drives/VFD
-PC with no ground connection
In that order, mostly.
Please Log in or Create an account to join the conversation.
- greg23_78
- Offline
- Premium Member
-
Less
More
- Posts: 142
- Thank you received: 7
13 Dec 2024 13:00 #316574
by greg23_78
Replied by greg23_78 on topic Solution fo "hm2 error finishing read" with no good PC
i will check.
the mesa card should be wire with the ground ?
the mesa card should be wire with the ground ?
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18105
- Thank you received: 5328
13 Dec 2024 15:04 #316580
by PCW
Replied by PCW on topic Solution fo "hm2 error finishing read" with no good PC
Look like more than just EMI causing lost Ethernet communications.
It actually it looks like the 7I97T card lost 5V power briefly,
since it does a full reset. I would check the 5V supply voltage,
current capability and connections.
In addition to tommylights suggestions, you might check that the contactor
contacts have arc suppressors, especially if they switch inductive loads.
It actually it looks like the 7I97T card lost 5V power briefly,
since it does a full reset. I would check the 5V supply voltage,
current capability and connections.
In addition to tommylights suggestions, you might check that the contactor
contacts have arc suppressors, especially if they switch inductive loads.
The following user(s) said Thank You: tommylight
Please Log in or Create an account to join the conversation.
- greg23_78
- Offline
- Premium Member
-
Less
More
- Posts: 142
- Thank you received: 7
13 Dec 2024 16:08 - 13 Dec 2024 16:10 #316585
by greg23_78
Replied by greg23_78 on topic Solution fo "hm2 error finishing read" with no good PC
well, I'm trying to locate the trouble, it's with the encoders: when I unplug them, there doesn't seem to be any restarting, and when I plug them back in, the default comes back from time to time.
my encoder is power by 5V
Could it be the power supply or the encoder ground?
below, is the power supply for the 7i97t card too weak?
my encoder is power by 5V
Could it be the power supply or the encoder ground?
below, is the power supply for the 7i97t card too weak?
Attachments:
Last edit: 13 Dec 2024 16:10 by greg23_78.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18105
- Thank you received: 5328
13 Dec 2024 16:21 #316587
by PCW
Replied by PCW on topic Solution fo "hm2 error finishing read" with no good PC
I would say that power supply is marginal
I would get a DIN mounted PS say a MDR20-5
Older encoders may draw considerable current
I would get a DIN mounted PS say a MDR20-5
Older encoders may draw considerable current
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21986
- Thank you received: 7486
13 Dec 2024 16:24 #316590
by tommylight
Replied by tommylight on topic Solution fo "hm2 error finishing read" with no good PC
Noooooooooooooooooo!!! 
Never use those power supplies for anything, ever, except powering LED lights maybe.
That is a non regulated transformer power supply with no output control at all, so voltage varies wildly with load, and is way above 5V at low loads when set to 5V.
Or look at it the other way, never use a 3$ power supply to power 1000$ equipment.
Get a MeanWell or Delta 5V power supply, at 20-30$ they are still cheap and can be found easily online.
In the meantime, if you have an old Samsung 5V charger, they were really good, the original ones, not the counterfeit ones.
Never use those power supplies for anything, ever, except powering LED lights maybe.
That is a non regulated transformer power supply with no output control at all, so voltage varies wildly with load, and is way above 5V at low loads when set to 5V.
Or look at it the other way, never use a 3$ power supply to power 1000$ equipment.
Get a MeanWell or Delta 5V power supply, at 20-30$ they are still cheap and can be found easily online.
In the meantime, if you have an old Samsung 5V charger, they were really good, the original ones, not the counterfeit ones.
Please Log in or Create an account to join the conversation.
- greg23_78
- Offline
- Premium Member
-
Less
More
- Posts: 142
- Thank you received: 7
13 Dec 2024 17:14 #316598
by greg23_78
Replied by greg23_78 on topic Solution fo "hm2 error finishing read" with no good PC
it's not common to have a 5V power supply, I'm going to order one, too bad it's not 24V because I have lots of power supplies
.
I replaced the power supply with a laboratory power supply (variable voltage).
It seems to work!
thanks for your advice!
I replaced the power supply with a laboratory power supply (variable voltage).
It seems to work!
thanks for your advice!