8 years 6 months ago #108749 by islander261
Replied by islander261 on topic Lagunmatic 3516-SX Retrofit
giz

Ok, this sounds similar to a problem I had recently. I also found an old Lagunamatic VMX500 drawing I had and the 120VAC circuit was not tied to chassis ground on one side. Disconnect both the input power and output wiring leaving the chassis ground connected on both power supplies. Then using an ohm meter check the resistance between each input/output terminal and chassis ground. There should be no low ohms connections. On the input side you may get a high ohms reading because of the input filter. Also check between the input and output terminals, again there should be no low ohms connection. One of the power supplies may have the output 0V or return terminal connected to chassis ground, this is done to help with noise reduction. If this is the case then you will need to either get a new power supply with isolated outputs or find a way to break the 0V/chassis ground connection.

While you have the power supply connections removed it is a good time to check all the DC/AC control circuits for faults to chassis ground or open circuits. Using an ohm meter trace each control circuit and verify it is good. Find all the problems and fix them. If the 120VAC circuit is wired the way the drawing I have shows there should be no connection to chassis ground on either leg. Make sure all DC relays have working (correct polarity) flyback diodes across the coils to protect the Mesa card.

John
The following user(s) said Thank You: giz

Please Log in or Create an account to join the conversation.

More
8 years 6 months ago #108752 by giz
Replied by giz on topic Lagunmatic 3516-SX Retrofit
Thanks a ton for the lengthy explanation John - this will help a lot this weekend when I'll be at the machine next!

Please Log in or Create an account to join the conversation.

More
8 years 6 months ago #108767 by lunada
Replied by lunada on topic Lagunmatic 3516-SX Retrofit
our machines do share neutral with 0v. Mine has been running like that for a year and a half now. Sorry i'm late to the party.
The following user(s) said Thank You: giz

Please Log in or Create an account to join the conversation.

More
8 years 6 months ago #108768 by giz
Replied by giz on topic Lagunmatic 3516-SX Retrofit

lunada wrote: our machines do share neutral with 0v. Mine has been running like that for a year and a half now. Sorry i'm late to the party.


No worries! Any insights on how you grounded TB5 field power on the 7i77?

Please Log in or Create an account to join the conversation.

More
8 years 6 months ago #108777 by lunada
Replied by lunada on topic Lagunmatic 3516-SX Retrofit
tb5? You mean TB2?
If you mean tb2, i came right off the 24v PS, and yes, it's still shared with neutral.

Please Log in or Create an account to join the conversation.

More
8 years 6 months ago #108817 by giz
Replied by giz on topic Lagunmatic 3516-SX Retrofit

lunada wrote: tb5? You mean TB2?
If you mean tb2, i came right off the 24v PS, and yes, it's still shared with neutral.


Yes, my mistake TB2. Thanks for confirming!