Parker AC10 via mb2hal: unreliable communication
- plovdiv
- Offline
- New Member
Less
More
- Posts: 14
- Thank you received: 0
30 Sep 2021 19:43 #221908
by plovdiv
Parker AC10 via mb2hal: unreliable communication was created by plovdiv
I'm connecting to a Parker AC10 VFD via USB/Modbus from linuxcnc 2.8.2.
But the connection is unreliable. There are sucessfull commands but a lot of errors too:
CRC
Connection timed out: select
Request for slave 128 ignored (not 1)
Looks like a physical i.e. wiring problem, but there is a nicely terminated twisted pair wiring between VFD and USBtoRS485.
Even more the same wiring worked well with the Parkers antecessor a huangyang VFD.
Any ideas?
But the connection is unreliable. There are sucessfull commands but a lot of errors too:
CRC
Connection timed out: select
Request for slave 128 ignored (not 1)
Looks like a physical i.e. wiring problem, but there is a nicely terminated twisted pair wiring between VFD and USBtoRS485.
Even more the same wiring worked well with the Parkers antecessor a huangyang VFD.
Any ideas?
Please Log in or Create an account to join the conversation.
- andypugh
- Offline
- Moderator
Less
More
- Posts: 23170
- Thank you received: 4860
01 Oct 2021 14:26 #221960
by andypugh
Replied by andypugh on topic Parker AC10 via mb2hal: unreliable communication
Not really a solution, but I see a lot of failed updates with my HY VFD under modbus control when I look at the output.
My solution is not to look at the output
The spindle seems to work just fine.
My solution is not to look at the output
The spindle seems to work just fine.
Please Log in or Create an account to join the conversation.
- plovdiv
- Offline
- New Member
Less
More
- Posts: 14
- Thank you received: 0
01 Oct 2021 14:49 #221964
by plovdiv
Optical isolated USB/RS485 and new wiring will be the next in poking around in the dark.
Replied by plovdiv on topic Parker AC10 via mb2hal: unreliable communication
I'ld love to not look, but dropout rate is to high.Not really a solution, but I see a lot of failed updates with my HY VFD under modbus control when I look at the output.
My solution is not to look at the output
The spindle seems to work just fine.
Optical isolated USB/RS485 and new wiring will be the next in poking around in the dark.
Please Log in or Create an account to join the conversation.
- persei8
- Offline
- Platinum Member
Less
More
- Posts: 386
- Thank you received: 121
01 Oct 2021 22:28 #221982
by persei8
Replied by persei8 on topic Parker AC10 via mb2hal: unreliable communication
How much different is that VFD from a Huanyang? If it's close, you are welcome to try out my custom made VFD HAL component. It was made specifically for a GT Series but if you can program a bit, it should be adaptable. It can go for hours without a single communication error.
Jim
Jim
Please Log in or Create an account to join the conversation.
- 0x2102
- Offline
- Elite Member
Less
More
- Posts: 210
- Thank you received: 75
02 Oct 2021 10:06 #222002
by 0x2102
Replied by 0x2102 on topic Parker AC10 via mb2hal: unreliable communication
Try using an RS485 adapter with A/B and GND connection instead of those simple USB with A/B only. I had similar issues before, if I remember correctly.
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Away
- Platinum Member
Less
More
- Posts: 4957
- Thank you received: 1441
07 Oct 2021 20:38 #222483
by Todd Zuercher
Replied by Todd Zuercher on topic Parker AC10 via mb2hal: unreliable communication
I had a problem with a bunch of Lenze ACTech drives, where if the commanded speed was less than the minimum setting set in the drive the communication would show a Modbus comm error in Linuxcnc. So when ever the spindle was stopped and the speed was set to zero I saw a constant string of comm errors. The slolution was to disable the minimum speed limit in the drive and do the limiting in Linuxcnc. No more comm errors.
Please Log in or Create an account to join the conversation.
- plovdiv
- Offline
- New Member
Less
More
- Posts: 14
- Thank you received: 0
07 Oct 2021 22:41 - 07 Oct 2021 22:43 #222499
by plovdiv
Replied by plovdiv on topic Parker AC10 via mb2hal: unreliable communication
Meanwhile I could solve the case by using another USB2RS485 adaptor..
The old one showed some weird behavior on the scope. With only 250 mV dU between A+ and B- it was inside standard but obviously outside the parker AC10s expectations. .
The new one (with GND connection by the way) showed of better
The old one showed some weird behavior on the scope. With only 250 mV dU between A+ and B- it was inside standard but obviously outside the parker AC10s expectations. .
The new one (with GND connection by the way) showed of better
Attachments:
Last edit: 07 Oct 2021 22:43 by plovdiv.