7i92t 7i77 problem
1 year 10 months ago #317625 by PCW
Replied by PCW on topic 7i92t 7i77 problem
OK that looks OK so the 7I92T I/O is likely OK
If you simply move the encoder plug from 7I77 encoder input 0 and
plug into encoder input 1, (drives disabled) Does the encoder 1 position
change when you rotate the encoder 0 motor shaft?
Also for encoder 2
What does it read?
If you watch GPIO 7..16  in the halshow watch tab, do they change/ flicker
when you rotate the shaft?
1 year 10 months ago #317627 by RK
Replied by RK on topic 7i92t 7i77 problem
Nothing happens when I move the encoder or the amplifier. It’s like the rest are not active except encoder 2 port. It flickers but does not read properly it just shows some change.
1 year 10 months ago #317628 by PCW
Are the 7I77 encoder jumpers set to match the encoder type?
(differential or single ended)
1 year 10 months ago #317630 by RK
Voltage looks good as well. Getting 4.9 volts at encoders and 23.9 volts at vin.
1 year 10 months ago #317631 by PCW
Are the encoders differential or single ended and is the 7I77 jumpered to match?
1 year 10 months ago #317633 by RK
PCW your a life saver!!
This project got shelved for a long time and I forgot about the jumpers. I see I only set the first axis. After setting the others I now have function. Thank you very much.
Time to create page: 0.182 seconds