5i25, 7i77 problem

More
11 Oct 2012 15:54 #25241 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
Andy, thanks for your response.

I did what you said and did this:

I do everything right, as cmorley says in pncconf I can see the inputs and outputs of "7i64" I read in the manual must encenderce the green "CR12" indicating that all is well but it does not, it stays on the red CR11.

Something I did not understand the cmorley response is this:

This will work as long as you Have the current bug fixes available from builbot or by compiling yourself.
If you do not you will Have to wait till the next bug fix release Which is supposed to come out soon.

Chris.

that may be bad?

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 15:55 #25242 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
halcmd: show pin
Component Pins:
Owner Type Dir Value Name
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-00
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-00-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-01
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-01-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-02
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-02-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-03
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-03-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-04
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-04-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-05
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-05-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-06
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-06-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-07
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-07-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-08
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-08-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-09
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-09-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-10
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-10-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-11
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-11-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-12
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-12-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-13
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-13-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-14
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-14-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-15
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-15-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-16
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-16-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-17
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-17-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-18
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-18-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-19
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-19-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-20
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-20-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-21
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-21-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-22
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-22-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-23
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-23-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-24
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-24-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-25
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-25-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-26
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-26-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-27
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-27-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-28
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-28-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-29
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-29-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-30
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-30-not
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-31
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-31-not
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-00
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-01
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-02
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-03
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-04
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-05
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-06
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-07
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-08
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-09
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-10
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-11
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-12
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-13
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-14
5 bit IN FALSE hm2_5i25.0.7i77.0.0.output-15
5 bit IN FALSE hm2_5i25.0.7i77.0.1.analogena
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout0
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout1
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout2
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout3
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout4
5 float IN 0 hm2_5i25.0.7i77.0.1.analogout5
5 bit IN FALSE hm2_5i25.0.7i77.0.1.spinena
5 s32 OUT 1 hm2_5i25.0.encoder.00.count
5 s32 OUT 0 hm2_5i25.0.encoder.00.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.00.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.00.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.00.latch-polarity
5 float OUT 1 hm2_5i25.0.encoder.00.position
5 float OUT 0 hm2_5i25.0.encoder.00.position-latched
5 s32 OUT 65536 hm2_5i25.0.encoder.00.rawcounts
5 s32 OUT 65535 hm2_5i25.0.encoder.00.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.00.reset
5 float OUT 0 hm2_5i25.0.encoder.00.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.01.count
5 s32 OUT 0 hm2_5i25.0.encoder.01.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.01.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.01.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.01.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.01.position
5 float OUT 0 hm2_5i25.0.encoder.01.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.01.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.01.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.01.reset
5 float OUT 0 hm2_5i25.0.encoder.01.velocity
5 s32 OUT -1 hm2_5i25.0.encoder.02.count
5 s32 OUT 0 hm2_5i25.0.encoder.02.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.02.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.02.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.02.latch-polarity
5 float OUT -1 hm2_5i25.0.encoder.02.position
5 float OUT 0 hm2_5i25.0.encoder.02.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.02.rawcounts
5 s32 OUT 1 hm2_5i25.0.encoder.02.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.02.reset
5 float OUT 0 hm2_5i25.0.encoder.02.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.03.count
5 s32 OUT 0 hm2_5i25.0.encoder.03.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.03.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.03.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.03.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.03.position
5 float OUT 0 hm2_5i25.0.encoder.03.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.03.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.03.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.03.reset
5 float OUT 0 hm2_5i25.0.encoder.03.velocity
5 s32 OUT -1 hm2_5i25.0.encoder.04.count
5 s32 OUT 0 hm2_5i25.0.encoder.04.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.04.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.04.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.04.latch-polarity
5 float OUT -1 hm2_5i25.0.encoder.04.position
5 float OUT 0 hm2_5i25.0.encoder.04.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.04.rawcounts
5 s32 OUT 1 hm2_5i25.0.encoder.04.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.04.reset
5 float OUT 0 hm2_5i25.0.encoder.04.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.05.count
5 s32 OUT 0 hm2_5i25.0.encoder.05.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.05.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.05.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.05.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.05.position
5 float OUT 0 hm2_5i25.0.encoder.05.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.05.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.05.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.05.reset
5 float OUT 0 hm2_5i25.0.encoder.05.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.06.count
5 s32 OUT 0 hm2_5i25.0.encoder.06.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.06.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.06.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.06.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.06.position
5 float OUT 0 hm2_5i25.0.encoder.06.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.06.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.06.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.06.reset
5 float OUT 0 hm2_5i25.0.encoder.06.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.07.count
5 s32 OUT 0 hm2_5i25.0.encoder.07.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.07.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.07.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.07.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.07.position
5 float OUT 0 hm2_5i25.0.encoder.07.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.07.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.07.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.07.reset
5 float OUT 0 hm2_5i25.0.encoder.07.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.08.count
5 s32 OUT 0 hm2_5i25.0.encoder.08.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.08.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.08.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.08.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.08.position
5 float OUT 0 hm2_5i25.0.encoder.08.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.08.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.08.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.08.reset
5 float OUT 0 hm2_5i25.0.encoder.08.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.09.count
5 s32 OUT 0 hm2_5i25.0.encoder.09.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.09.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.09.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.09.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.09.position
5 float OUT 0 hm2_5i25.0.encoder.09.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.09.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.09.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.09.reset
5 float OUT 0 hm2_5i25.0.encoder.09.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.10.count
5 s32 OUT 0 hm2_5i25.0.encoder.10.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.10.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.10.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.10.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.10.position
5 float OUT 0 hm2_5i25.0.encoder.10.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.10.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.10.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.10.reset
5 float OUT 0 hm2_5i25.0.encoder.10.velocity
5 s32 OUT 0 hm2_5i25.0.encoder.11.count
5 s32 OUT 0 hm2_5i25.0.encoder.11.count-latched
5 bit I/O FALSE hm2_5i25.0.encoder.11.index-enable
5 bit IN FALSE hm2_5i25.0.encoder.11.latch-enable
5 bit IN FALSE hm2_5i25.0.encoder.11.latch-polarity
5 float OUT 0 hm2_5i25.0.encoder.11.position
5 float OUT 0 hm2_5i25.0.encoder.11.position-latched
5 s32 OUT 0 hm2_5i25.0.encoder.11.rawcounts
5 s32 OUT 0 hm2_5i25.0.encoder.11.rawlatch
5 bit IN FALSE hm2_5i25.0.encoder.11.reset
5 float OUT 0 hm2_5i25.0.encoder.11.velocity
5 bit OUT TRUE hm2_5i25.0.gpio.000.in
5 bit OUT FALSE hm2_5i25.0.gpio.000.in_not
5 bit IN FALSE hm2_5i25.0.gpio.000.out
5 bit OUT TRUE hm2_5i25.0.gpio.001.in
5 bit OUT FALSE hm2_5i25.0.gpio.001.in_not
5 bit IN FALSE hm2_5i25.0.gpio.001.out
5 bit OUT TRUE hm2_5i25.0.gpio.002.in
5 bit OUT FALSE hm2_5i25.0.gpio.002.in_not
5 bit IN FALSE hm2_5i25.0.gpio.002.out
5 bit OUT TRUE hm2_5i25.0.gpio.003.in
5 bit OUT FALSE hm2_5i25.0.gpio.003.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.004.in
5 bit OUT FALSE hm2_5i25.0.gpio.004.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.005.in
5 bit OUT FALSE hm2_5i25.0.gpio.005.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.006.in
5 bit OUT FALSE hm2_5i25.0.gpio.006.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.007.in
5 bit OUT FALSE hm2_5i25.0.gpio.007.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.008.in
5 bit OUT TRUE hm2_5i25.0.gpio.008.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.009.in
5 bit OUT TRUE hm2_5i25.0.gpio.009.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.010.in
5 bit OUT TRUE hm2_5i25.0.gpio.010.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.011.in
5 bit OUT TRUE hm2_5i25.0.gpio.011.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.012.in
5 bit OUT TRUE hm2_5i25.0.gpio.012.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.013.in
5 bit OUT TRUE hm2_5i25.0.gpio.013.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.014.in
5 bit OUT TRUE hm2_5i25.0.gpio.014.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.015.in
5 bit OUT TRUE hm2_5i25.0.gpio.015.in_not
5 bit OUT FALSE hm2_5i25.0.gpio.016.in
5 bit OUT TRUE hm2_5i25.0.gpio.016.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.017.in
5 bit OUT FALSE hm2_5i25.0.gpio.017.in_not
5 bit IN FALSE hm2_5i25.0.gpio.017.out
5 bit OUT TRUE hm2_5i25.0.gpio.018.in
5 bit OUT FALSE hm2_5i25.0.gpio.018.in_not
5 bit IN FALSE hm2_5i25.0.gpio.018.out
5 bit OUT TRUE hm2_5i25.0.gpio.019.in
5 bit OUT FALSE hm2_5i25.0.gpio.019.in_not
5 bit IN FALSE hm2_5i25.0.gpio.019.out
5 bit OUT TRUE hm2_5i25.0.gpio.020.in
5 bit OUT FALSE hm2_5i25.0.gpio.020.in_not
5 bit IN FALSE hm2_5i25.0.gpio.020.out
5 bit OUT TRUE hm2_5i25.0.gpio.021.in
5 bit OUT FALSE hm2_5i25.0.gpio.021.in_not
5 bit IN FALSE hm2_5i25.0.gpio.021.out
5 bit OUT TRUE hm2_5i25.0.gpio.022.in
5 bit OUT FALSE hm2_5i25.0.gpio.022.in_not
5 bit IN FALSE hm2_5i25.0.gpio.022.out
5 bit OUT TRUE hm2_5i25.0.gpio.023.in
5 bit OUT FALSE hm2_5i25.0.gpio.023.in_not
5 bit IN FALSE hm2_5i25.0.gpio.023.out
5 bit OUT TRUE hm2_5i25.0.gpio.024.in
5 bit OUT FALSE hm2_5i25.0.gpio.024.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.025.in
5 bit OUT FALSE hm2_5i25.0.gpio.025.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.026.in
5 bit OUT FALSE hm2_5i25.0.gpio.026.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.027.in
5 bit OUT FALSE hm2_5i25.0.gpio.027.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.028.in
5 bit OUT FALSE hm2_5i25.0.gpio.028.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.029.in
5 bit OUT FALSE hm2_5i25.0.gpio.029.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.030.in
5 bit OUT FALSE hm2_5i25.0.gpio.030.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.031.in
5 bit OUT FALSE hm2_5i25.0.gpio.031.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.032.in
5 bit OUT FALSE hm2_5i25.0.gpio.032.in_not
5 bit OUT TRUE hm2_5i25.0.gpio.033.in
5 bit OUT FALSE hm2_5i25.0.gpio.033.in_not
5 bit IN FALSE hm2_5i25.0.led.CR01
5 bit IN FALSE hm2_5i25.0.led.CR02
5 u32 IN 0x00000000 hm2_5i25.0.sserial.channel
5 u32 IN 0x00000000 hm2_5i25.0.sserial.parameter
5 u32 IN 0x00000000 hm2_5i25.0.sserial.port
5 u32 OUT 0x000000D7 hm2_5i25.0.sserial.port-0.fault-count
5 u32 OUT 0x00000020 hm2_5i25.0.sserial.port-0.port_state
5 bit IN TRUE hm2_5i25.0.sserial.port-0.run
5 bit IN FALSE hm2_5i25.0.sserial.read
5 u32 OUT 0x00000000 hm2_5i25.0.sserial.state
5 u32 IN 0x00000000 hm2_5i25.0.sserial.value
5 bit IN FALSE hm2_5i25.0.sserial.write
5 bit I/O TRUE hm2_5i25.0.watchdog.has_bit

halcmd:

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 16:21 #25243 by PCW
Replied by PCW on topic Re:5i25, 7i77 problem
can you try running this set if hal and ini files:

freeby.mesanet.com/7i77.zip

unzip them into (home)/linuxcnc/configs/hm2-servo

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 16:32 - 11 Oct 2012 16:42 #25244 by PCW
Replied by PCW on topic Re:5i25, 7i77 problem
Also is the 7I64 jumpered properly? I think Default is USB interface

(make sure W1,W2,W3 are up/down/up)
Last edit: 11 Oct 2012 16:42 by PCW.

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 16:36 #25245 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
blessed language, limiting ... besides that not much ... lol

But I'll keep trying ...

"5i25" and "7i77" perfect work.

"5i25", "7i77", "7i64" works, linux smoothly opens in PnCConf, I can see the inputs and outputs of "7i64".

settings as I do?

I am guided by what Chris said in a thread:

chris wrote:

Here is how to get what you want.
on the table I / O - config page September the number of encoder to 6 and the number of channels sserial to 3 and press 'accept changes'

this gets rid of the second 7i77 board components and Allows them to be GPIO (You Will See That tab on the connector 2)

Now on the connector 3 tab look for the smartserial # 2 combo box. second box down left side.
select the 7i64 board and a tab will Appear - 'smart serial # 2'
This is the tab to configure the 7i64 board.

This will work as long as you Have the current bug fixes available from builbot or by compiling yourself.
If you do not you will Have to wait till the next bug fix release Which is supposed to come out soon.

Chris

but when I open linuxcnc find nothing about "7i64". of the rest everything is perfect.

I recognize the "7i64"


seriously sorry that trouble.

thank you very much.

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 16:40 #25246 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
The real question is:

as I view the inputs and outputs of the "7i64"?

everything seems fine but not see them.
Attachments:

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 16:53 - 11 Oct 2012 16:59 #25247 by PCW
Replied by PCW on topic Re:5i25, 7i77 problem
Is the 7I64 jumpered properly?

as I mentioned before The default jumpering is for USB interface:
(W1,W2,W3 = UP,UP,UP)
for sserial/LinuxCNC you need 2.5 MBaud serial:
(W1,W2,W3 = UP.DOWN,UP)
Last edit: 11 Oct 2012 16:59 by PCW. Reason: ommision

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 17:00 #25248 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
Peter.


I have not moved the jumpers this as manufactured

buy the serial cable and connect it to TB2 of "7i77"

right now you only the red LED "CR11"


thanks

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 17:01 #25249 by PCW
Replied by PCW on topic Re:5i25, 7i77 problem
Did you set W1,W2,W3 to UP,DOWN.UP?

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 17:03 #25250 by andypugh
Replied by andypugh on topic Re:5i25, 7i77 problem
jlviloria wrote:

halcmd: show pin
Component Pins:
Owner Type Dir Value Name
5 bit OUT FALSE hm2_5i25.0.7i77.0.0.input-00
5 bit OUT TRUE hm2_5i25.0.7i77.0.0.input-00-not


The 7i64 pins should be listed here.
It seems that Hostmot2 isn't seeing the 7i64.

I think you might be being confused by the interaction between PNCConf and the rest of LinuxCNC.

PNCConf has no idea what smart-serial cards you have attached. It tries to set up the card you tell it is attached, whether or not that card is attached and working.

I think that PCW might have guessed the problem, is your 7i64 set with the jumpers for serial connection and for cable power?

W1 W2 W3
UP DOWN DOWN 1.25 MBAUD
UP DOWN UP 2.5 MBAUD FOR SSERIAL
UP UP DOWN 5.0 MBAUD
UP UP UP USB INTERFACE SELECTED

You need the jumpers W2 W3 W4 to be UP - DOWN - UP.

Please Log in or Create an account to join the conversation.