5i25, 7i77 problem

More
11 Oct 2012 17:46 #25251 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
thank you very much friends ....

I know it's something simple, but for me it is very valuable all this information.


forward in my project.

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 23:01 #25255 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
New Here bothering.

I have three concerns.

1. Looking at the HAL that Rick (LAIR82) published in a thread,

www.linuxcnc.org/media/kunena/attachments/legacy/files/rick.txt

I realize that the external output signal and external signal input, place the vast majority of "net" prepending #. this would indicate that only a comment?
of the machine and mine are like a lot. but that just confuses me see connections no comments.


2. thanks to you I could see the inputs and outputs of the "7i64" but are different from the "7i77" I look like this:

net min-x <= hm2_5i25.0.7i64.0.2.digin.02.in

digin not nothing wrong?


3. I want to try the servomotors and the "DC spindle motor" without connecting anything else yet, or home sensor, limit switch, nothing more. that's possible?
bone without linuxcnc throw me any error?

thanks in advance.

File Attachment:

File Name: HidroCNC.hal
File Size:9 KB
Attachments:

Please Log in or Create an account to join the conversation.

More
11 Oct 2012 23:17 #25257 by andypugh
Replied by andypugh on topic Re:5i25, 7i77 problem
jlviloria wrote:

I realize that the external output signal and external signal input, place the vast majority of "net" prepending #. this would indicate that only a comment?

Yes, those lines in the HAL have been disabled.
It is quite common to do that if you are unsure what you are doing. Leave the old HAL command there as reference, and add a new version. If it all goes wrong you can then easily uncomment the old version.
One might expect to eventually delete all the disabled commands.

2. thanks to you I could see the inputs and outputs of the "7i64" but are different from the "7i77" I look like this:
net min-x <= hm2_5i25.0.7i64.0.2.digin.02.in

Yes, the pin names on the 7i64 are different. This is because the 7i64 driver was written before Mesa started making cards which choose their own pin names.
In the next version of LinuxCNC the pin names of the 7i64 will change to be consistent (sorry about that, but you will need to edit your HAL at that point)

3. I want to try the servomotors and the "DC spindle motor" without connecting anything else yet, or home sensor, limit switch, nothing more. that's possible?
bone without linuxcnc throw me any error?

Yes, just comment/disable out all the homing stuff in the iNI and HAL files.

Please Log in or Create an account to join the conversation.

More
18 Oct 2012 02:56 #25409 by jlviloria
Replied by jlviloria on topic Re:5i25, 7i77 problem
Peter wrote:
Looks fine except all the logical control signals are 120VAC input.
Its pretty likely that these are already connected to a 2IO4B rack so the 24VDC-->120VAC level shift may already be done for you.

This, and the state machine way the control inputs work probably means
you need to use 7I77 or 7I64 outputs for the 24 V signals that drive the
2IO4B that drives the 4 spindle control signals (manual page 21)

Also note figure 4.8 on page 57 This should be close to how it is wired now
So the first step on the spindle interfacing is tracing whats already there
(or better yet reading if you have the machine manual)

You want to retain as much of the original safety and interlock wiring as possible

a 50 HP spindle can kill you in milliseconds




www.reliance.com/pdf/drives/instruction_manuals/D3867.pdf


Peter,

greetings,

Friend, I am applying 120VAC at terminals 33, 44, and 32, but I notice that the motor runs, but rotates with difficulty. The question should not only operate the contactor M, hoping that 326 and 157 into action? or am I wrong?

any advice helps.

thanks

Please Log in or Create an account to join the conversation.

More
18 Oct 2012 17:13 #25416 by PCW
Replied by PCW on topic Re:5i25, 7i77 problem
There are three logical inputs (ignoring jog)

32 start
33 stop
44 coast

These are all momentary inputs as the drive state is latched.
Only one should be asserted at a time, and removed after its applied
so if you apply 120VAC to start (32) and then remove it
the drive should be in run state and respond to analog speed commands on pin 326/157

Please Log in or Create an account to join the conversation.