Huanyang VFD and Mesa 7i76e stuck at 6000 rpm
6 years 3 months ago #175346 by PCW
So you really only need 3 points for lincurve (you could actually do the same thing with the scale component since you are just offsetting the analog output by 6000 )
setp lincurve.0.x-val-00 0
setp lincurve.0.y-val-00 0
setp lincurve.0.x-val-01 6000
setp lincurve.0.y-val-01 0
setp lincurve.0.x-val-02 24000
setp lincurve.0.y-val-02 24000
The following user(s) said Thank You: Stran_ge
6 years 3 months ago - 6 years 3 months ago #175347 by Stran_ge
i changed the hal part and now when i start the spindle it starts at 6000 but i cant change the speed anymore.
I can start stop and change direction nothing else.
The Output voltage stays the same whatever i input via m3 sxxxxx
i appreciate the help so far, im trying to get this working correctly for the past 2 days
Last edit: 6 years 3 months ago by Stran_ge.
6 years 3 months ago - 6 years 3 months ago #175348 by PCW
I would check lincurves output and x,y values
That is, if you have a single X value of 24000 paired with a Y value of 24000
there's not any reason you should not get a lincurve output of 24000 with an input of 24000
Last edit: 6 years 3 months ago by PCW.
6 years 3 months ago - 6 years 3 months ago #175349 by Stran_ge
so as you can see on the attached image i tell the vfd/spindle to go 7700 rpm but it stays at 6000 ( i tired that with numerous values).
with the previous hal config. i was able to change the speeds even tho they were far off.
I cant attach my image even tho it is small enough for some reason so i can only post an imgur link, sry.
https://imgur.com/a/H25buvZ
Do you think it would help if edit my Ini min_limit to 6000 ?
My vfd is set up to 100hz ~ 400Hz with 0~10v but software is prob. thinking 0~400 Hz is 0~10v
6 years 3 months ago - 6 years 3 months ago #175350 by PCW
Can you post your current hal/ini files?
I just tested this and linucurve acts as expected with the values I posted,
that is
loadrt lincurve personality=3
addf lincurve.0 servo-thread
outputs 0 at a commanded RPM of 6000 and 24000 at a commanded RPM of 24000
and a correct interpolated value for commanded RPM values between 6000 and 24000
6 years 3 months ago - 6 years 3 months ago #175351 by Stran_ge
PCW i think i found my error here, i still had loadrt lincurve personality=4
i changed it to 3 and now im only round about 200-300 rpm off of what i want.
Is that acceptable or still bad ?
File Name: configv5_2...21-2.ini
File Size:5.15 KB
File Name: configv5_2...21-2.hal
File Size:12.57 KB