upgraded from 2.5 to 2.6 tuning issues
- clkeck1
18 Dec 2014 10:31 #54108
by clkeck1
upgraded from 2.5 to 2.6 tuning issues was created by clkeck1
My mother board bit the dust so I upgraded to an ASUS J1800I which required Wheezy and 2.6
I updated all the 7i64 pins and fired up the machine knowing I had to retune.
The axis were much louder and on the edge of being unstable during jog and homing.
I loaded the tuning repeat program and started to tune. To get the machine stable the P values are 1/4 of what they used to be and the both the motor and plots are very noisy.
I tried setting pins pid.N.error-previous-target back to false like in 2.5 and this impacts the FF1 but everything is still noisy.
Is there something that I'm missing?
- clkeck1
18 Dec 2014 10:40 #54109
by clkeck1
Replied by clkeck1 on topic upgraded from 2.5 to 2.6 tuning issues
files attached
- Thank you received: 5263
18 Dec 2014 13:07 #54112
Replied by PCW on topic upgraded from 2.5 to 2.6 tuning issues
There should be no difference at all between 2.5 and 2.6 tuning wise except for the pid.N.error-previous-target.
There was a bug in muxed encoder firmware where encoder velocity was not calculated properly (scaling was wrong)
this would cause your D term to need to be updated if you used encoder velocity pin for pid.N.feedback-deriv
but your hal file does not seem to use the encoder velocity pins so I dont know whats going on.
You might try connecting/tuning the D term with pid.N.feedback-deriv connected (which should be superior
to the d/dt created velocity used by the PID comp if the pid.N.feedback-deriv is unconnected)
- clkeck1
18 Dec 2014 21:30 #54128
by clkeck1
So just add the following for each axis?
setp pid.N.feedback-deriv hm2_5i23.0.encoder.0N.velocity
- clkeck1
18 Dec 2014 21:39 #54129
by clkeck1
19 Dec 2014 00:22 - 19 Dec 2014 00:33 #54135
if your encoder channels match your PID component numbers it would be like:
setp pid.0.feedback-deriv hm2_5i23.0.encoder.0.velocity
setp pid.1.feedback-deriv hm2_5i23.0.encoder.1.velocity
setp pid.2.feedback-deriv hm2_5i23.0.encoder.2.velocity
Last edit: 19 Dec 2014 00:33 by PCW.
- clkeck1
19 Dec 2014 00:41 #54136
by clkeck1
Ok I will give it a try later today
- clkeck1
19 Dec 2014 03:42 #54145
by clkeck1
net motor.02.vel-fb hm2_5i23.0.encoder.02.velocity => pid.2.feedback-deriv
added the above line to the hal file.
no help any other ideas?
was there maybe a filter change on the 7i48?
19 Dec 2014 03:55 - 19 Dec 2014 03:58 #54146
The 7I48 filters are hardware so other than component failure should stay the same
I would not expect _any_ tuning change going from 2.5 to 2.6 other that needing to set pid.N.error-previous-target. false
maybe something else in your system changed
Note that on the axis you showed in the HALScope plot you have no D term (while the other axis have significant D term)
will have no effect unless you have some D term
Last edit: 19 Dec 2014 03:58 by PCW.
- clkeck1
19 Dec 2014 04:22 #54147
by clkeck1
I tried D from .001 up to 1 and it doesn't change the amplitude of the noise I started with the Z axis because it was acting the worst.
I even tried switching the 7i48 over to cable power to isolate it from the machine power supply and put it on the computer power supply.
The plot shows a constant 300IPM move and as expected when PID output (pink) is high F-error (red) is also high. and when one is low so is the other.
What can be causing this?
Time to create page: 0.108 seconds