1 or 2 dedicated 120VAC circuits for my CNC?
3 years 11 months ago #257540 by spumco
Internet search for "NEC Ampacity Chart" will give you a good idea.  Based on your amps, plus some overhead:
Main to 120VAC terminal block - 10AWG
120 block to contactor - 12AWG
Contactor to 60v PSU and router relay - 12AWG
120 block to 24v PSU - 18AWG
All the DC circuits can be 20AWG
Neutrals & grounds sizes to match the hot line for various circuits.
10AWG & larger is a pain to work with - super stiff and needs to be pre-bent before sticking in terminals & components.  Anything smaller than 20 or 22 is also a pain to work with - too small for clumsy hands.
The power cord from the box to the recepticle should be 10/3 SJOOW (30A).
To put the icing on the cake, get a copy (internet) of NFPA-79.  That has all the standard wire colors for various circuit voltages & functions, as well as a good reference for terminology.
The following user(s) said Thank You: Sray69
3 years 11 months ago #257541 by spumco
That reminds me, I would like to figure out a way to switch my dust collection OFF during a fault, E-stop, end of job, etc. I haven't thought through the logistics yet. I may want to have it turn on when the router comes on but not sure. There may be times when I don't want it on while running a job. Either way I would like to figure out how I can accomplish this. The dust collection unit is on the other side of the wall that the CNC is on. I have dust collection conduit running through the wall at the ceiling level above the CNC. I thought I could run 24V +/- from a digital out on the Mesa up the wall and attach it to the conduit and run it through the wall to the outlet that the collector is plugged into. I thought about just getting one of the IoT Power Strips and connect the 24V wires to it. I am sure this is not the cheapest way but definitely the quickest/easiest way.
That IOT power strip can't handle a 24v signal.  It takes either 3.3/5vdc or 120vac.
You could put another relay in the box, feed it 120vac from the contactor output, and control it with 24vdc from the Mesa.  The relay's 120vac output goes over to the IOT thing and turns the dust collector on/off.  The relay can be a really low-amp SPST thing - I bet the IOT strip wouldn't pull 0.5A to turn on.
The dust collector is now programmable with an M-code, and the relay shuts off during an estop.  Bamma-jamma...
3 years 11 months ago #257542 by Sray69
Thanks for the wire info.
Yeah I have a copy. The first time I tried to read through it it was not real easy to follow. I will have to look through it again now that I am starting to understand things better.
Based on the spec sheet...
The universal control voltage 3-48VDC or 12-120VAC allows control from virtually any micro or AC source.
But it also states that it is only rated for "AC loads of up to 12 Amps total". The dust collector would not fire up with that many amps. I am intrigued by the idea of designing something myself someday but for now I will just have to turn it on and off manually. Need to keep focused.
Thanks!
3 years 11 months ago - 3 years 11 months ago #257554 by spumco
Ahh - I misremembered the spec sheet.
Easy option - mount a small enclosure on the wall where the dust collector mounts and install a contactor in it.  Feed it with 120vac.  Run a 24vdc signal from Mesa to it - can be a small 18awg cord.
If you're worried about drawing too many amps or EMI or something, you can isolate the Mesa by using a small relay to switch the 24vdc.  i.e. Mesa to relay coil, and 24vdc through the relay contacts to the contactor.
Basically a home-brewed version of the IOT thing, but with proper components.
Last edit: 3 years 11 months ago by spumco.
3 years 11 months ago #257593 by Sray69
Yeah that is exactly my thoughts.
I happen to come across this New - Open Box contactor that looks pretty decent. I was thinking that if this is a decent contactor I could use it either for the dust collector or the router and use the Fuji for the other. Much more reasonable price than the Fuji was.
Eaton Contactor 1NC/3NO IP20 24VDC 15.5A 7.5kW DILMC15-01
3 years 11 months ago #257684 by spumco
No eBay APP ID and/or Cert ID defined in Kunena configurationEaton makes good stuff.  I'd have no problems sticking that in one of my machines.
Spotted these too:
[url][/url]
Time to create page: 0.160 seconds