7i77 CR16 red
- nadine
13 Jan 2019 13:02 #124073
by nadine
7i77 CR16 red was created by nadine
Hi
I just startet with LinuxCNC, got a MESA 7i76e (REV.B ) and a 7i77 (REV.C) card and wired the basic things. I've installed the latest Debian + LinuxCNC + mesaflash as BigJohnT descibed it (thank you, btw, very helpful guide) and played arround with 3 working axis with a little stepper. Also all 7 encoder inputs are working and I see 6 analog outputs on the 7i77.
Unfortunately I can't see the field IOs on the 7i77 and the CR16 LED is red. The W4 and W12 are in the left position.
The firmware I wrote to the 7i76e is this one: 7i76e_7i76x1_7i77x1D.bit (change date: 13 Sep 2014)
I attached the dmesg (cleared before LinuxCNC was executed) and the terminal output from starting and closing LinuxCNC.
What did I miss?
Nadine
What did I miss?
Nadine
- Online
- Thank you received: 1476
14 Jan 2019 03:12 #124136
Replied by Todd Zuercher on topic 7i77 CR16 red
Do you have the field power attached to both the 7i77 and the 7i76e? The Smartserial connections will not be seen unless they have power supplied to them.
- nadine
14 Jan 2019 09:12 #124147
by nadine
Replied by nadine on topic 7i77 CR16 red
Yes, I have. I actually can see anything on the 7i76e, only no field IOs on the 7i77. CR16 is only on, if field power is connected to the 7i77. Regarding to the manual, CR16 means:
"Field I/O fault; The red LED CR16 indicates a watchdog fault, which is
expected before host communications are established."
Therefore I think the problem is software related.
- Thank you received: 5328
14 Jan 2019 14:53 #124155
Replied by PCW on topic 7i77 CR16 red
can you post your hal and ini files?
- nadine
14 Jan 2019 15:16 #124157
by nadine
- Thank you received: 7483
14 Jan 2019 15:37 #124161
Replied by tommylight on topic 7i77 CR16 red
Not sure, but you should check this line where the sserial address is.
loadrt hm2_eth board_ip="192.168.1.121" config=" num_encoders=7 num_pwmgens=-1 num_stepgens=5 sserial_port_0=2000"
14 Jan 2019 15:39 #124162
Looks OK, Not sure whats going on, here are a few guesses:
Possible bad cable/connection to 7I77
If you changed W12 did you power cycle the 7I77s field power?
Is the 7I77s W1 in the left hand position?
Marginal 5V power on 7I77
Conflct in 7I76E/7I77 5V power jumpers
- nadine
14 Jan 2019 16:43 #124165
by nadine
OK, thank you.
The cable is new, but I'll check with another cable (takes a bit time).
Never changed W12, but power cycled the board incl. field power several times.
W1 on 7i77 is in the right hand position with 24V connected to the pins 1 + 5 of TB2 and ground to pin 8.
TB1 on 7i77 has 5,11V. Should I measure that at another point?
Jumpers on 7i76e:
W7: down
W6: up
W1: right
W8: left
W4: up
W5: up
Jumpers on 7i77:
W5: right
W4: left
W1: right
W12: left
Maybe this is important: CR16 turns red immediately (<1s) after switching on power. 5V power for both cards is from the same power supply. Same with 24V, so they power up at the same time. Is there a dependency, that the FPGA-card has to be ready before powering the other one?
Jumpers on 7i76e:
W7: down
W6: up
W1: right
W8: left
W4: up
W5: up
Jumpers on 7i77:
W5: right
W4: left
W1: right
W12: left
14 Jan 2019 17:11 #124170
[/quote]
Maybe this is important: CR16 turns red immediately (<1s) after switching on power. 5V power for both cards is from the same power supply. Same with 24V, so they power up at the same time. Is there a dependency, that the FPGA-card has to be ready before powering the other one?[/quote]
No there's no power dependencies other than 5V and field power must be present before starting LinuxCNC
- nadine
14 Jan 2019 17:47 #124174
by nadine
OK
Before I try another cable: Should CR16 light up if no DB25 cable is connected?
Time to create page: 0.109 seconds