Ohmic3 hal file errors
- bevins
- Thank you received: 338
01 Apr 2021 08:20 #204373
by bevins
I get no signal in Linuxcnc
Replied by bevins on topic Ohmic3 hal file errors
The ohmic probe I still have the same issue. So something is not hooked up correctly in hal.
What issue?
- Thank you received: 4140
01 Apr 2021 08:28 #204374
Replied by rodw on topic Ohmic3 hal file errors
There are a number of pins in ohmic3 that you can monitor in halshow for debugging. I'm not in a linux pc now but I would check that you can see the ohmic volts move from 0 to 24 volts or there abouts. If you jog down at the smallest resolution (0.01 mm for me) you should be able to see the voltage ramp up on each click as contact is made.
Then choose a threshold that suits your hardware.
- bevins
01 Apr 2021 23:40 #204449
by bevins
OK but I am getting nothing at encoder.01.velocity.
03 Apr 2021 07:19 #204595
If that is the case, I think it will be becasue the encoder is not set up and enabled in your hal file.
03 Apr 2021 07:29 #204596
We talked about this earlier in this thread.
forum.linuxcnc.org/38-general-linuxcnc-q...rors?start=30#204298
- bevins
03 Apr 2021 14:17 #204623
by bevins
Yes and I added the lines and it still didnt work.
- snowgoer540
- Thank you received: 900
03 Apr 2021 15:35 #204631
by snowgoer540
When I looked last it seemed like your Hal files were correct.
If you’re seeing no velocity on .01, then there is likely something wrong with the wiring from the output of the thcad to the encoder input on your 7i92.
Replied by snowgoer540 on topic Ohmic3 hal file errors
03 Apr 2021 23:30 #204684
You said the THCAD was flashing so that indicates its generating a frequency.
If it was on 0 volts, there would be a reading on the encoder of about 3800 or 1/32 whatever the calibration sticker says.
Have you got the 1/32 jumper selected on the THCAD?
have you installed the correct bit file?
Can you see the additional encoders in halshow to confirm?
If you are still seeing 0, then its a wiring error. The THCAD should be attached to encoder 1 in Hal which is the Encoder B signal in the mesa docs. (not familiar with your card)
Alternatively if you are using a 7i77, then it would have its own encoder so use the encoder A signals on the appropriately numbered encoder.
- bevins
04 Apr 2021 15:22 - 04 Apr 2021 15:23 #204771
by bevins
I am using 7i92-7i76
I have verified the correct bit file.
I have verified the wiring. swapped out with thc THCAD,
It is flashing yellow like the THC thcad
I do have 1/32 jumper selected.
Last edit: 04 Apr 2021 15:23 by bevins.
- bevins
04 Apr 2021 15:25 #204772
by bevins
I will take Tommy's advice and redo a config and use ohmic2 for now.
I have all the parts wires and relays.
Time to create page: 0.252 seconds