mb2hal: trying to control a Siemens Sinamics V20 VFD
- flawapawacrew
- Offline
- Junior Member
Less
More
- Posts: 20
- Thank you received: 3
07 Sep 2021 21:40 #219884
by flawapawacrew
mb2hal: trying to control a Siemens Sinamics V20 VFD was created by flawapawacrew
Hello everyone,
I am new to the forum and to linuxcnc. I am currently trying to connect with a Sinamics VFD using mb2hal.
My setup is a RaspberryPi 4 with the "official" linuxcnc raspibian build with USB to RS485 adapter. This is connected to the VDF using a twisted pair and GND, and all terminating resistors, etc... are connected as recommended by the Operating instructions (attached). I scoped the signals, double, triple checked the parameters set in the VFD. I am 90% sure the communication setup in hardware is sane.
I wrote a very simple .ini file and .hal file to test the communication (attached). The .ini file was written based on the the Operating instructions for number of bits, partiy, etc...
I useto start the hal component. Unfortunately, I get an error message after sending the first command (returned by the VFD if I am not mistaken):
The complete output of the shell command is attached ("shell_mb2hal_output_short.txt"). This is with all debug levels set to 3.
From what I understand, the register addresses are wrongly defined...? I followed the table at page 142 of the Operating Instructions.
Is there something I am missing here?
Also, I noted an error at the beginning:
Which makes no sense to me as transaction 00 is defined and we read two registers. Note that this error is not present for mb2hal.00.01
Again, am I missing something?
I thank you in advance for your insight!
Cheers,
Flawa
I am new to the forum and to linuxcnc. I am currently trying to connect with a Sinamics VFD using mb2hal.
My setup is a RaspberryPi 4 with the "official" linuxcnc raspibian build with USB to RS485 adapter. This is connected to the VDF using a twisted pair and GND, and all terminating resistors, etc... are connected as recommended by the Operating instructions (attached). I scoped the signals, double, triple checked the parameters set in the VFD. I am 90% sure the communication setup in hardware is sane.
I wrote a very simple .ini file and .hal file to test the communication (attached). The .ini file was written based on the the Operating instructions for number of bits, partiy, etc...
I use
halcmd -f sinamics_mb2hal.hal
ERROR Illegal data address
The complete output of the shell command is attached ("shell_mb2hal_output_short.txt"). This is with all debug levels set to 3.
From what I understand, the register addresses are wrongly defined...? I followed the table at page 142 of the Operating Instructions.
Is there something I am missing here?
Also, I noted an error at the beginning:
sinamics_mb2hal.hal:8: Pin 'mb2hal.00.00' does not exist
Which makes no sense to me as transaction 00 is defined and we read two registers. Note that this error is not present for mb2hal.00.01
Again, am I missing something?
I thank you in advance for your insight!
Cheers,
Flawa
Please Log in or Create an account to join the conversation.
- flawapawacrew
- Offline
- Junior Member
Less
More
- Posts: 20
- Thank you received: 3
07 Sep 2021 21:51 #219887
by flawapawacrew
Replied by flawapawacrew on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
Hello,
Apparently the attached pdf was not uploaded. The Operating Instructions can be consulted online at this address :
www.manualslib.com/manual/1203313/Siemen...html?page=142#manual
Cheers,
Flawa
Apparently the attached pdf was not uploaded. The Operating Instructions can be consulted online at this address :
www.manualslib.com/manual/1203313/Siemen...html?page=142#manual
Cheers,
Flawa
Please Log in or Create an account to join the conversation.
- andypugh
- Offline
- Moderator
Less
More
- Posts: 23170
- Thank you received: 4860
12 Sep 2021 13:27 #220306
by andypugh
Replied by andypugh on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
It is possible that the error you see is caised by the earlier error:
Is it possible to fix that? If you insert a line "show pin" straight after the loadrt mb2hal line then you will get a dump of all the pins that exist at that point in the output.
sinamics_mb2hal.hal:8: Pin 'mb2hal.00.00' does not exist
Is it possible to fix that? If you insert a line "show pin" straight after the loadrt mb2hal line then you will get a dump of all the pins that exist at that point in the output.
Please Log in or Create an account to join the conversation.
- flawapawacrew
- Offline
- Junior Member
Less
More
- Posts: 20
- Thank you received: 3
13 Sep 2021 16:29 #220458
by flawapawacrew
Replied by flawapawacrew on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
Hi andypugh,
thank you for your answer!
Using, I was able to understand that there is aandpin. Using either of them did get rid of the aforementionned error. So that's a step forward!
Unfortunaltely, theerror still shows up. I tried with different register addresses in the range 40000 - 40038 with no success. An example of modbus communication found on the siemens website (support.industry.siemens.com/cs/document...h-hmi?dti=0&lc=en-US) seems to confirm that I am using the correct range of addresses.
I will probably factory reset and re-configure, just to be sure.
I am also wondering if there is a precise order in which one needs to access the drive's registers...
Will keep you posted.
Cheers,
Thierry
thank you for your answer!
Using
show pin
mb2hal.00.00.int
mb2hal.00.00.float
Unfortunaltely, the
Illegal data address
I will probably factory reset and re-configure, just to be sure.
I am also wondering if there is a precise order in which one needs to access the drive's registers...
Will keep you posted.
Cheers,
Thierry
Please Log in or Create an account to join the conversation.
- Aciera
- Offline
- Administrator
Less
More
- Posts: 4006
- Thank you received: 1730
13 Sep 2021 16:54 - 13 Sep 2021 16:57 #220463
by Aciera
Replied by Aciera on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
I think in mb2hal you can turn on a debug mode that shows you the actual data being sent and recieved. That might be helpful to compare with the example modbus communication. So maybe set INIT_DEBUG=3
[MB2HAL_INIT]
#OPTIONAL: Debug level of init and INI file parsing.
# 0 = silent.
# 1 = error messages (default).
# 2 = OK confirmation messages.
# 3 = debugging messages.
INIT_DEBUG=3
Last edit: 13 Sep 2021 16:57 by Aciera.
Please Log in or Create an account to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
Less
More
- Posts: 4957
- Thank you received: 1441
15 Sep 2021 16:17 #220713
by Todd Zuercher
Replied by Todd Zuercher on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
You might try using 38 (or 37 or 39) instead of 40038 as the element#.
I know the drives I'm using work that way (but they are not Siemens). The documentation lists the addresses as 400XX, but in my config I subract 40,000 from the number. So for address 40008, I'd use FIRST_ELEMENT=8 for 40038, I'd use FIRST_ELEMENT=38.
I know the drives I'm using work that way (but they are not Siemens). The documentation lists the addresses as 400XX, but in my config I subract 40,000 from the number. So for address 40008, I'd use FIRST_ELEMENT=8 for 40038, I'd use FIRST_ELEMENT=38.
Please Log in or Create an account to join the conversation.
- flawapawacrew
- Offline
- Junior Member
Less
More
- Posts: 20
- Thank you received: 3
17 Sep 2021 15:51 - 17 Sep 2021 15:53 #220915
by flawapawacrew
Replied by flawapawacrew on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
Thank you folks for the advice!
@Aciera: I am using INIT_DEBUG=3. This is the typical output I get (here trying to access register 40011):
[/code]
As you see the only error is the illegal data address, everything else seems to be fine. And the response bytes are consistent. This leads me to suppose that the hardware comm is fine (since everything is consistent), and the sent bytes and answer bytes are coherent with what should be sent and received (I checked that).
@Todd: Ok, will try! I just thought "It can't be that simple"...
@Aciera: I am using INIT_DEBUG=3. This is the typical output I get (here trying to access register 40011):
[code]halcmd -f sinamics_mb2hal.hal
...
mb2hal parse_ini_file OK: parse_transaction_section 0 OK
mb2hal main OK: parse_ini_file done OK
mb2hal init_mb_links DEBUG: LINK 0 (RTU) link_type[0] device[/dev/ttyUSB0] baud[9600] data[8] parity[E] stop[1] fd[-1]
mb2hal main OK: init_gbl.mb_link done OK
mb2hal init_mb_tx DEBUG: MB_TX 0 lk_n[0] tx_n[0] cfg_dbg[3] lk_dbg[1] t_inc[0.100] nxt_t[0.000]
mb2hal main OK: init_gbl.mb_tx done OK
mb2hal create_each_mb_tx_hal_pins DEBUG: mb_tx_num [0] pin_name [mb2hal.accel_time.num_errors]
mb2hal create_each_mb_tx_hal_pins DEBUG: mb_tx_num [0] pin_name [mb2hal.accel_time.00]
mb2hal main OK: HAL components created OK
mb2hal main OK: Link thread loop and logic 0 created OK
mb2hal main OK: mb2hal is running
Component Pins:
Owner Type Dir Value Name
4 float OUT 0 mb2hal.accel_time.00.float
4 s32 OUT 0 mb2hal.accel_time.00.int
4 u32 OUT 0x00000000 mb2hal.accel_time.num_errors
mb2hal link_loop_and_logic DEBUG: mb_tx_num[0] mb_links[0] thread[0] fd[-1] going to TEST availability
mb2hal link_loop_and_logic DEBUG: mb_tx_num[0] mb_links[0] thread[0] fd[-1] going to TEST connection
mb2hal get_tx_connection DEBUG: mb_tx_num[0] mb_links[0] new connection -> fd[4]
mb2hal link_loop_and_logic DEBUG: mb_tx_num[0] mb_links[0] thread[0] fd[4] lk_dbg[1] going to EXECUTE transaction
[b]mb2hal fnct_03_read_holding_registers DEBUG: mb_tx[0] mb_links[0] slave[1] fd[4] 1st_addr[40011] nelem[1]
[01][03][9C][4B][00][01][DA][4C]
Waiting for a confirmation...
<01><83><02><C0><F1>
ERROR Illegal data address
mb2hal fnct_03_read_holding_registers ERR: mb_tx[0] mb_links[0] slave[1] = ret[-1] fd[4]
mb2hal link_loop_and_logic ERR: mb_tx_num[0] mb_links[0] thread[0] fd[4] transaction failure, num_errors[1]
Bytes flushed (0)
mb2hal link_loop_and_logic DEBUG: mb_tx_num[0] mb_links[0] thread[0] fd[4] SERIAL_DELAY_MS activated [0]
mb2hal link_loop_and_logic DEBUG: mb_tx_num[0] mb_links[0] thread[0] fd[4] gbl.slowdown activated [1.000]
...
sudo pkill mb2hal
mb2hal quit_signal DEBUG: signal [15] received
mb2hal quit_cleanup DEBUG: started
mb2hal quit_cleanup DEBUG: unloading HAL module [4] ret[0]
mb2hal quit_cleanup DEBUG: done OK
mb2hal main OK: going to exit![/b]
As you see the only error is the illegal data address, everything else seems to be fine. And the response bytes are consistent. This leads me to suppose that the hardware comm is fine (since everything is consistent), and the sent bytes and answer bytes are coherent with what should be sent and received (I checked that).
@Todd: Ok, will try! I just thought "It can't be that simple"...
Last edit: 17 Sep 2021 15:53 by flawapawacrew.
Please Log in or Create an account to join the conversation.
- Aciera
- Offline
- Administrator
Less
More
- Posts: 4006
- Thank you received: 1730
17 Sep 2021 16:01 #220917
by Aciera
Replied by Aciera on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
Ah yes, I'm sorry I didn't catch that you were using debug level 3 in your first post. And yes your hardware and com parameters seem correct given the answer from the vfd.
I couldn't find the example but I expected it to show an actual Modbus telegram. My approach would be to try and replicate that telegram and verify that using the debug information:[01][03][9C][4B][00][01][DA][4C]An example of modbus communication found on the siemens website
Please Log in or Create an account to join the conversation.
- tommylight
- Online
- Moderator
Less
More
- Posts: 19471
- Thank you received: 6530
17 Sep 2021 23:43 #220962
by tommylight
Replied by tommylight on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
Spammer booted.
Please Log in or Create an account to join the conversation.
- flawapawacrew
- Offline
- Junior Member
Less
More
- Posts: 20
- Thank you received: 3
20 Sep 2021 16:44 #221207
by flawapawacrew
Replied by flawapawacrew on topic mb2hal: trying to control a Siemens Sinamics V20 VFD
So it turns out Todd was correct. I tried to access register 11 (instead of 40011) and the communication went through! Thanks Todd
I now have to figure out how to write my hal file in order to send the correct commands.
I might need your insight on that, but I have to do some reading and testing first
Cheers!
I now have to figure out how to write my hal file in order to send the correct commands.
I might need your insight on that, but I have to do some reading and testing first
Cheers!