8 years 7 months ago #107163 by aleksamc
Works great with OutPUT_SCALE =1000. Thank you hundred times, Peter.
I wonder why it differs from OutPut_Scale from linuxcnc docs:
linuxcnc.org/docs/2.4/html/examples_spindle.html
There is wrong explanation.
8 years 7 months ago #107164 by PCW
Replied by PCW on topic Configuration 7i92m_7i76x1D
How the output is scaled depends on the output device
The PWM example is closer to the way the 7I76 (and all sserial devices) scale outputs
Pretty sure pncconf sets this up correctly, though it might name the scaling constant a little
differently for clarity (say Full_Scale_Output instead of Output_Scale)
8 years 5 months ago #110103 by aleksamc
For a long time of work under this CNC machine, we have turned on electricity at it and and made wirst moves.
Now make configurations for machine.
Now I try to configure spindle and I've seen that spindle output of 7i76 depends of temperatre a lot.
When I configured it at first time, it was 9 of March, and it was cold, It gave me 10V, but now, when it's hot, at 100% it gives me only 80%.
MAX_OUTPUT = 4000
OUTPUT_SCALE = 4000
OUTPUT_MIN_LIMIT = 0
OUTPUT_MAX_LIMIT = 4000
May be I'm wrong, because I has some error mstakes when I start machine and turn on linuxcnc:
hm2/hm2_7i92.0: smart serial card
hm2_7i92.0.7i76.0.0 remote error = (27) Over current
hm2_7i92.0.7i76.0.0 remote error = (8) remote fault
But all axes work fine, everything OK.
Does it could be solver of this problems?
8 years 5 months ago #110115 by PCW
The output PWM circuit should be quite stable (it should drift no more than a fraction of a percent over 0 to 70C temperature)
I would check that the input voltage is not changing
Did the sserial errors start at the same time? the over current error may indicate an external short or a damaged output driver chip
8 years 5 months ago #110127 by aleksamc
Over current temperature error few times was blinking. After some time and restart, I don't see it any more. Also, I've inverted output GPIO outputs if step signals.
I will check input voltage but I think it's OK.
Max voltage from resistor is still 8V.
8 years 5 months ago - 8 years 5 months ago #110131 by PCW
So if the supply is 10V and you get 8V out (and you have full scale in hal)
Then there is a hardware problem (damaged OP-AMP etc)
The PWM circuit is pretty simple OPTO --> CMOS gate --> passive RC filter --> rail-rail opamp