- Thank you received: 7491
Elumatec SBZ 130/01 retrofit
9 years 9 months ago #85718
Replied by tommylight on topic Elumatec SBZ 130/01 retrofit
Finally started working on this machine, got rid of the old controls and computer and mounted the Mesa cards. Getting familiar with all the inner workings as much as possible on a non functioning machine, and planing everything humanly possible upfront, so here is a short burst of info:
-motors have brakes, tacho and serial absolute encoders
-long axis has a separate absolute encoder with separate rack and pinion, brake on the motor and pneumatic brake on the rails, had separate control
-spindle looks like having 1to1 ratio on tool 1 so good for rigid tapping, can not check other tools for now
-tool changer has another brake and a clutch inside
-a lot of pneumatic valves, relays, end switches, pressure sensors, clamps etc
After a detailed check, found out that the long axis encoder has "direction" wire, others do not.
So it looks like the serial absolute encoders on 3 normal axis and spindle are usual "clock +-" and "data+-" type, so hopefully they can be made to work with 7i74, and this is the first thing i have to check.
The setup is: 6i25=>7i77&7i74=>7i70&7i71, already flashed with 5i25_7i77_7i74.bit file
---how do i go about using the 7i74 as half SSI and half SSerial? I need 4 encoders and 7i70 and 7i71, nothing more
Attaching some pictures of the old and the new.
Regards,
Tom
P.S.
Attached pictures of the encoders, the one on the long X axis is not the same as the other 4, it has a wire labelled "richtung" meaning direction???
Regards,
Tom
P.S.
The following user(s) said Thank You: tmoeti
- Thank you received: 5334
9 years 9 months ago #85721
Replied by PCW on topic Elumatec SBZ 130/01 retrofit
I'm pretty sure you need a custom bitfile for this.
I'll try and cobble one together tomorrow, a bit too much red wine tonight...
probably named 5i25_7I77_7i74_ssi_ss.bit
9 years 9 months ago #85746
Thank you very much Peter.
9 years 9 months ago #85763
freeby.mesanet.com/77ssiss.zip
Has the 5i25/6i25 bitfile and the new pinout file source code
P3 --> 7I77
P2 --> 7I74 (channels 0..3= SSI 4..7= Sserial)
Not tested, better to test with a 6i25 than 5I25 since a 6I25 can be boostrapped without
JTAG if a non-workin bitfile is loaded
P3 --> 7I77
9 years 9 months ago #85766
Nice nice NICE !!!!
Thank you very much Peter, will give that a try tomorrow, now if only i had a simmilar config to test encoder reading.......ah wishful thinking!
I forsee a lot of reading.........of a thread here about serial encoders and 7i74, over 10 forum pages long. Oh joy.
Today i wired the 3 phase AC servo drive that drives the spindle to the analog output 4 of 7i77 and made it run on both directions, speed control working properly and working enable. Will move it to Aout5 tomorow as it has separate enable.
Wiring advice:
When connecting enable signals to 7i77, before connecting the enable wires, use a 1Kohm ( i used a 470 ohm ) resistor acros them, it should enable the drive and the motor should start turning slowly. If that works, connect those 2 wires to the 7i77 enable, but wire the resistor in series with one of the wires. That way even if the polarity is wrong, it will not destroy the 7i77 optocoupler.
PCW correct me if i am wrong on the above.
Again thank you all.
Wiring advice:
9 years 9 months ago - 9 years 9 months ago #85769
Typically you will not hurt the optocouplers by wiring them backwards (it will just be stuck on)
This is because typical load currents for drive enables and VFD enables are only a few mA
or few 10s of mA for small 24V relays
HOWEVER wiring them into a shorted load (or wrong polarity flyback diode on a relay)
will definitely kill them so I think its good to test the wiring with a mechanical switch
replacing the OPTO when first setting up.
The low value series resistor is also a good idea for first time testing
Last edit: 9 years 9 months ago by PCW.
Time to create page: 0.606 seconds