Pairing up Mesa 7i76e with VFD Delta C2000
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
09 Jan 2019 12:45 #123825
by andypugh
Replied by andypugh on topic Pairing up Mesa 7i76e with VFD Delta C2000
A line driver into a high-impedence oscilloscope might give a higher than specified voltage. You could try loading it with a resistor. It is rated 50mA, so I would first try a 1k resistor (5mA) and see if that squares-up and reduces the peak and noise in the signal.
To figure out the resolution, just watch the counts in halmeter, rotate the spindle 10x by hand, and divide the change in counts by 10.
To figure out the resolution, just watch the counts in halmeter, rotate the spindle 10x by hand, and divide the change in counts by 10.
Please Log in or Create an account to join the conversation.
- vmihalca
- Offline
- Platinum Member
-
Less
More
- Posts: 346
- Thank you received: 22
09 Jan 2019 19:02 #123852
by vmihalca
Replied by vmihalca on topic Pairing up Mesa 7i76e with VFD Delta C2000
I did some more research being helped by a friend that's more into electronics.
We have discovered that the board outputs differential outputs, and there is no common ground between the phases.
Also we discovered that the voltage is from -7.5 to +7.5 and not from 0 to 15
We created a voltage divider using two 500ohm resistors, and filtered the noise with a 1nF capacitor. We ended up with a 4.8v peak to peak.
But this voltage is from -2.4 to +2.4 and not from 0-4.8v.
Can I feed this signal into the mesa board? Or do I need a 0-5v signal.
We have discovered that the board outputs differential outputs, and there is no common ground between the phases.
Also we discovered that the voltage is from -7.5 to +7.5 and not from 0 to 15
We created a voltage divider using two 500ohm resistors, and filtered the noise with a 1nF capacitor. We ended up with a 4.8v peak to peak.
But this voltage is from -2.4 to +2.4 and not from 0-4.8v.
Can I feed this signal into the mesa board? Or do I need a 0-5v signal.
Please Log in or Create an account to join the conversation.
- andypugh
-
- Offline
- Moderator
-
Less
More
- Posts: 19898
- Thank you received: 4655
09 Jan 2019 19:47 #123861
by andypugh
Replied by andypugh on topic Pairing up Mesa 7i76e with VFD Delta C2000
The Mesa inputs are selectable TTL or Differential, IIRC.
What you have is differential. (which is a good thing, it is more noise-resistant)
manual: www.mesanet.com/pdf/parallel/7i76man.pdf
Page 2 W4 W5 W6
What you have is differential. (which is a good thing, it is more noise-resistant)
manual: www.mesanet.com/pdf/parallel/7i76man.pdf
Page 2 W4 W5 W6
Please Log in or Create an account to join the conversation.
- vmihalca
- Offline
- Platinum Member
-
Less
More
- Posts: 346
- Thank you received: 22
09 Jan 2019 20:21 #123867
by vmihalca
Replied by vmihalca on topic Pairing up Mesa 7i76e with VFD Delta C2000
So you're saying its ok to feed into the mesa board a signal that' from - to + and not from 0 to +?
I would not like to get my board fried.
I thought I need to supply a signal between 0 and 5V
I would not like to get my board fried.
I thought I need to supply a signal between 0 and 5V
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18111
- Thank you received: 5330
09 Jan 2019 20:34 - 09 Jan 2019 20:35 #123868
by PCW
Replied by PCW on topic Pairing up Mesa 7i76e with VFD Delta C2000
7I76E differential encoder inputs have a common mode range of -7 to +12V
and a differential sensitivity of 200 mV, and a maximum differential voltage of 5V,
So the will take positive and negative inputs as long as they are in that range
You must make sure that no input exceeds +13V or -9V or you may damage the input receiver chip. If you have large signals and large noise spikes, you should use your input divider. Note that the 7I76E encoder inputs are terminated with a 120 Ohm resistor across the differential inputs pairs, so you may need to adjust your divider accordingly. As long as you get about 2V across the inputs its good.
and a differential sensitivity of 200 mV, and a maximum differential voltage of 5V,
So the will take positive and negative inputs as long as they are in that range
You must make sure that no input exceeds +13V or -9V or you may damage the input receiver chip. If you have large signals and large noise spikes, you should use your input divider. Note that the 7I76E encoder inputs are terminated with a 120 Ohm resistor across the differential inputs pairs, so you may need to adjust your divider accordingly. As long as you get about 2V across the inputs its good.
Last edit: 09 Jan 2019 20:35 by PCW.
Please Log in or Create an account to join the conversation.
- vmihalca
- Offline
- Platinum Member
-
Less
More
- Posts: 346
- Thank you received: 22
10 Jan 2019 21:52 - 10 Jan 2019 21:54 #123924
by vmihalca
Replied by vmihalca on topic Pairing up Mesa 7i76e with VFD Delta C2000
I have made today some measurements and some tests. I have discovered that the encoder board has a SG pin that I assumed it comes from 'signal ground'.
I have connected the ground of the probes to the ground, and then connected the probes to the A and A' with a 110ohm resistor between them to simulate the internal resistor that mesa has.
See the measurements in the pics below.
I am wondering if the noise that appears in the signal can get out of the -7/+12v range and if this could affect the mesa board.
Given how the signal looks now, do you think its safe to connect the wires to the Mesa's encoder input?
Also, do I need to connect the ground from the encoder to the GND encoder pin on the Mesa?
I have connected the ground of the probes to the ground, and then connected the probes to the A and A' with a 110ohm resistor between them to simulate the internal resistor that mesa has.
See the measurements in the pics below.
I am wondering if the noise that appears in the signal can get out of the -7/+12v range and if this could affect the mesa board.
Given how the signal looks now, do you think its safe to connect the wires to the Mesa's encoder input?
Also, do I need to connect the ground from the encoder to the GND encoder pin on the Mesa?
Last edit: 10 Jan 2019 21:54 by vmihalca.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21997
- Thank you received: 7488
10 Jan 2019 22:30 #123926
by tommylight
Replied by tommylight on topic Pairing up Mesa 7i76e with VFD Delta C2000
I would not connect that. You are using non shielded cable for signalling, shielding is a must in such machines, to many devices making to much electrical noise.
BTW, cable shielding should be connected only on one side, not both. Usually on the electronics side.
BTW, cable shielding should be connected only on one side, not both. Usually on the electronics side.
Please Log in or Create an account to join the conversation.
- vmihalca
- Offline
- Platinum Member
-
Less
More
- Posts: 346
- Thank you received: 22
10 Jan 2019 23:08 #123931
by vmihalca
Replied by vmihalca on topic Pairing up Mesa 7i76e with VFD Delta C2000
Do you think a double shielded FTP cable would do it?
You said about connecting only one side; here the sides I have are the Mesa board and this board that converts from the resolver signal.
To which of them should I connect the shielding? Where should I connect the shielding? To ground?
Sorry if I'm asking stupid questions, I'm a very beginner with the electronics.
You said about connecting only one side; here the sides I have are the Mesa board and this board that converts from the resolver signal.
To which of them should I connect the shielding? Where should I connect the shielding? To ground?
Sorry if I'm asking stupid questions, I'm a very beginner with the electronics.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 21997
- Thank you received: 7488
11 Jan 2019 14:33 #123975
by tommylight
Replied by tommylight on topic Pairing up Mesa 7i76e with VFD Delta C2000
Electronics side.
Encoders or resolvers should be grounded at the Mesa input side ( or other board ), motors should be grounded at the driver side, sensors and switches also at the board side, etc
Encoders or resolvers should be grounded at the Mesa input side ( or other board ), motors should be grounded at the driver side, sensors and switches also at the board side, etc
Please Log in or Create an account to join the conversation.
- vmihalca
- Offline
- Platinum Member
-
Less
More
- Posts: 346
- Thank you received: 22
18 Jan 2019 09:49 #124393
by vmihalca
Replied by vmihalca on topic Pairing up Mesa 7i76e with VFD Delta C2000
I have replaced the cable with a double shielded S/FTP cable.
Now the signal is more clear, it has some spikes and the VPP is 8v so between the -7v..+12v range. The base is 300mV and the top is 3.6v
Between the A and A' I have added a 110ohm resistor to simulate the internal resistor of the mesa board.
I assume its safe to connect now the encoder to the mesa board.
So my encoder has differential outputs, so I will have 6 wires for A,A' B,B' Z,Z' and GND.
Is it ok to connect the ground of the encoder to the ground on the encoder port on the mesa?
Now the signal is more clear, it has some spikes and the VPP is 8v so between the -7v..+12v range. The base is 300mV and the top is 3.6v
Between the A and A' I have added a 110ohm resistor to simulate the internal resistor of the mesa board.
I assume its safe to connect now the encoder to the mesa board.
So my encoder has differential outputs, so I will have 6 wires for A,A' B,B' Z,Z' and GND.
Is it ok to connect the ground of the encoder to the ground on the encoder port on the mesa?
Please Log in or Create an account to join the conversation.