7I97T joint following error
- tommylight
-
- Away
- Moderator
-
Less
More
- Posts: 19902
- Thank you received: 6738
20 Mar 2025 21:15 #324379
by tommylight
Replied by tommylight on topic 7I97T joint following error
Use PncConf to create a basic minimal config for 7i92 with 7i77, then we can modify it to fit the 7i97T and give it a try.
Simple 3 axis config, no spindle, no I/O, no MPG, nothing else.
Also upload one of the existing configs that run so we can get the card addresses.
Simple 3 axis config, no spindle, no I/O, no MPG, nothing else.
Also upload one of the existing configs that run so we can get the card addresses.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18356
- Thank you received: 5004
20 Mar 2025 22:56 - 20 Mar 2025 23:02 #324385
by PCW
Replied by PCW on topic 7I97T joint following error
The issue is this:
[JOINT_0]
CARD = 0
TAB = 0
AXIS = X
MIN_LIMIT = 0
MAX_LIMIT = 30
MAX_VELOCITY = 200
MAX_ACCELERATION = 200
TYPE = LINEAR
SCALE = 40000
ANALOG_SCALE_MAX = 10
ANALOG_MIN_LIMIT = -10
ANALOG_MAX_LIMIT = 10
That sets the PWM scale so you need an error of 20000 inches to
get a full scale (10V) output, or 2 inches to get a mV.
Ideally the PWM scale should be set to the velocity in machine units per second
at 10V. This way, the FF1 term is known to be 1.00
[JOINT_0]
CARD = 0
TAB = 0
AXIS = X
MIN_LIMIT = 0
MAX_LIMIT = 30
MAX_VELOCITY = 200
MAX_ACCELERATION = 200
TYPE = LINEAR
SCALE = 40000
ANALOG_SCALE_MAX = 10
ANALOG_MIN_LIMIT = -10
ANALOG_MAX_LIMIT = 10
That sets the PWM scale so you need an error of 20000 inches to
get a full scale (10V) output, or 2 inches to get a mV.
Ideally the PWM scale should be set to the velocity in machine units per second
at 10V. This way, the FF1 term is known to be 1.00
Last edit: 20 Mar 2025 23:02 by PCW.
Please Log in or Create an account to join the conversation.
- Tinker
- Offline
- Junior Member
-
Less
More
- Posts: 30
- Thank you received: 1
20 Mar 2025 23:26 #324386
by Tinker
Replied by Tinker on topic 7I97T joint following error
That definitely made a huge difference!! What would be a good SCALE number to start out with? or how does one calculate it?
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18356
- Thank you received: 5004
21 Mar 2025 00:06 - 21 Mar 2025 00:07 #324390
by PCW
Replied by PCW on topic 7I97T joint following error
The scale is generally either left in volts (10) or better
set to the machine units per second at 10V
That is, you have a inch machine, so motion calculations
are in inches per second, if you set the PWM scale to
the velocity (in inches per second) you get at 10V,
then all the PID numbers are scaled in motion units
(inches per second) and FF1 (the most important
PID tuning parameter for velocity mode servos)
is 1.00
set to the machine units per second at 10V
That is, you have a inch machine, so motion calculations
are in inches per second, if you set the PWM scale to
the velocity (in inches per second) you get at 10V,
then all the PID numbers are scaled in motion units
(inches per second) and FF1 (the most important
PID tuning parameter for velocity mode servos)
is 1.00
Last edit: 21 Mar 2025 00:07 by PCW.
Please Log in or Create an account to join the conversation.
- Tinker
- Offline
- Junior Member
-
Less
More
- Posts: 30
- Thank you received: 1
24 Mar 2025 21:42 #324828
by Tinker
Replied by Tinker on topic 7I97T joint following error
So say my servos are 2400 RPM @10V with 2/1 reduction and 5 tpi ball screws, would that be the basic formula used to come up with velocity in IPS?
Please Log in or Create an account to join the conversation.
- Tinker
- Offline
- Junior Member
-
Less
More
- Posts: 30
- Thank you received: 1
24 Mar 2025 21:45 #324829
by Tinker
Replied by Tinker on topic 7I97T joint following error
Basically 4 IPS would be my scale number if I'm understanding you correctly..
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18356
- Thank you received: 5004
24 Mar 2025 22:16 #324836
by PCW
Replied by PCW on topic 7I97T joint following error
Yes, at motor 2400 RPM the ballscrew would turn at 1200 RPM (20 TPS)
and 20 TPS * 0.2 IPT = 4 IPS
and 20 TPS * 0.2 IPT = 4 IPS
The following user(s) said Thank You: Tinker