Ethercat drives not responding, mesa error finishing read

More
02 Dec 2025 18:19 #339658 by nanowhat
The next time I see that error, I will try those things.

Please Log in or Create an account to join the conversation.

More
04 Dec 2025 17:34 #339737 by nanowhat
$lcecObject.pll-error-count is holding at 2. I haven't seen it increase yet.

I want to read some more data from the drives, and it won't work. See attached iX7NH.xml, line 23. I want to see the temperature values from the drive, but I can't read them. As shown, where pdoEntry idx="260B", the drive stays in PREOP (see dmesg output in dmesg260B.txt). If I change the index to "2606", the drive will go to OP (see dmesg output in dmesg2606.txt) and I can see the number through HAL (that I don't want). Registers 2606 and 260B are both 16 bit signed integers.
Any of 260B, 260C, or 260D (all temperature sensors in the servo system) have the same effect.


I can read the values manually with "ethercat upload -p0 -t int16 0x260B 0" and I get some number.
The drive manual says I can read up to 10 registers with one TxPDO: I have 6.
It also says that I am limited to 28 bytes in one TxPDO: I have 13.
How do I do this?
Attachments:

Please Log in or Create an account to join the conversation.

More
04 Dec 2025 18:20 #339739 by Hakan
With pll-reset-count steady at to 2 it should be fine.

Try to locate temperature sensors in the pdo listing from "ethercat pdos".
I suspect you are addressing a sdo with 2605 and that won't work.
You'll find out from the ethercat pdos listing.

Please Log in or Create an account to join the conversation.

More
04 Dec 2025 18:30 - 04 Dec 2025 18:33 #339740 by nanowhat
Output from "ethercat pdos" in attached file.

0x2605 works just fine: that's the DC link voltage and I can read that from all 3 drives.
0x260B does not.

The drive manual doesn't discuss SDOs, or whether some data index is a PDO or SDO. I would hope a temperature sensor would be continuously readable, which would require it to be a PDO.
Attachments:
Last edit: 04 Dec 2025 18:33 by nanowhat.

Please Log in or Create an account to join the conversation.

More
04 Dec 2025 18:44 #339742 by nanowhat
I figured it out. The manual doesn't explicitly mention SDOs but it does say whether an index can be assigned to a PDO and I ignored that information the first time around.
260B, 260C, and 260D cannot be assigned to a PDO.

Is there another way of getting this information into HAL, or do I need to write a custom component?
Attachments:

Please Log in or Create an account to join the conversation.

More
04 Dec 2025 20:35 #339746 by Hakan
There is no way to read an SDO value into hal as far as I know.
But as you say it wouldn't be too hard to write a user-space hal component in python
the runs the command "ethercat -p n upload 0x2608 0", parses the output and returns a value.
I mean, in principle.
 

Please Log in or Create an account to join the conversation.

More
15 Dec 2025 23:51 #340155 by nanowhat
I've put together that userspace component to get the temperatures, and it works just fine.
Attachments:
The following user(s) said Thank You: besriworld, Hakan

Please Log in or Create an account to join the conversation.