PCW has shared the THCAD rise time delay here and its super quick. Z axis Acceleration is an important tuning parameter for THC I found. and the AMP connectors are available from RS Components in Oz. You are going to smash this Phill!
The following user(s) said Thank You: phillc54
Please Log in or Create an account to join the conversation.
- phillc54
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 5711
- Thank you received: 2100
23 Apr 2019 06:57 - 23 Apr 2019 06:57 #131607
by phillc54
Replied by phillc54 on topic plasma control panel
I have come up with this wiring diagram, all comments welcome.
I haven't forgotten limit switches, I don't really want to use them as I haven't on any of my other machines and not had too many dramas..
Actually this is the first time I will use home switches, I usually just eyeball matchmarks which has served well in the past.
Cheers, Phill.
I haven't forgotten limit switches, I don't really want to use them as I haven't on any of my other machines and not had too many dramas..
Actually this is the first time I will use home switches, I usually just eyeball matchmarks which has served well in the past.
Cheers, Phill.
Last edit: 23 Apr 2019 06:57 by phillc54.
Please Log in or Create an account to join the conversation.
- tommylight
-
- Offline
- Moderator
-
Less
More
- Posts: 22006
- Thank you received: 7489
23 Apr 2019 09:29 #131614
by tommylight
Replied by tommylight on topic plasma control panel
That looks all good.
The following user(s) said Thank You: phillc54
Please Log in or Create an account to join the conversation.
- thefabricator03
-
- Visitor
-
23 Apr 2019 09:34 #131615
by thefabricator03
Replied by thefabricator03 on topic plasma control panel
Phil,
Just wondering what program you used to draw up that diagram, I am about to convert my machine to open source linux from CommandCNC and I need to draw up something very similar. You wouldnt happen to have the diagram in a DWG format you could share?
Just wondering what program you used to draw up that diagram, I am about to convert my machine to open source linux from CommandCNC and I need to draw up something very similar. You wouldnt happen to have the diagram in a DWG format you could share?
Please Log in or Create an account to join the conversation.
- phillc54
-
Topic Author
- Offline
- Platinum Member
-
Less
More
- Posts: 5711
- Thank you received: 2100
23 Apr 2019 09:55 #131618
by phillc54
Replied by phillc54 on topic plasma control panel
Here you go, the forum doesn't like DWG so just take .TXT off the end. If that is no good I can do DXF. I use QCAD-Pro.
Cheers, Phill.
Cheers, Phill.
Please Log in or Create an account to join the conversation.
- rodw
-
- Offline
- Platinum Member
-
Less
More
- Posts: 12161
- Thank you received: 4151
23 Apr 2019 10:06 - 23 Apr 2019 10:07 #131620
by rodw
Replied by rodw on topic plasma control panel
Phil, Aside from adding limit switches it looks good! You got the inputs so put them in where you can. I use PNP prox sensors so all wiring is on the gantry. On the Z axis, I ran a 9 wire cable up with DB9 connectors. 2 wires for 24 volts and that left 7 inputs.
PCW has suggested you can use the onboard spindle relay to turn the torch on but I do it the way you do it.
To be compliant you are not meant to use relays on an estop circuit as it introduces a further point of failure. I used a cheap estop from Jaycar which has two sides to it. One sends a signal to the 7i76e and the other side trjps power to the stepper controller 48 v power supply.
Then I added a pendant and another estop button which are all chained together in hal using estop-latch.
If I did estop again I would use one of these switches becasue you can clip on additional switch mechanisims behind the button.
oceancontrols.com.au/HNR-241.html
Finally a friend suggested to add a led indicator for each power supply in the system (Plus I have one on the gantry). I have found that very useful isolating faults. You wonder why its not working and then you check all the power is up before panicking!. I added another LED on the gantry breakout box power.
PCW has suggested you can use the onboard spindle relay to turn the torch on but I do it the way you do it.
To be compliant you are not meant to use relays on an estop circuit as it introduces a further point of failure. I used a cheap estop from Jaycar which has two sides to it. One sends a signal to the 7i76e and the other side trjps power to the stepper controller 48 v power supply.
Then I added a pendant and another estop button which are all chained together in hal using estop-latch.
If I did estop again I would use one of these switches becasue you can clip on additional switch mechanisims behind the button.
oceancontrols.com.au/HNR-241.html
Finally a friend suggested to add a led indicator for each power supply in the system (Plus I have one on the gantry). I have found that very useful isolating faults. You wonder why its not working and then you check all the power is up before panicking!. I added another LED on the gantry breakout box power.
Last edit: 23 Apr 2019 10:07 by rodw.
The following user(s) said Thank You: phillc54
Please Log in or Create an account to join the conversation.
- thefabricator03
-
- Visitor
-
20 May 2019 23:51 - 21 May 2019 23:35 #134415
by thefabricator03
Replied by thefabricator03 on topic plasma control panel
Hi Guys,
Instead of starting a new topic I thought I would add to this one,
Can I get some help proof reading my wiring diagram,
There might be some things that stand out that I should change, Just want to be sure before wiring up the beast!
Instead of starting a new topic I thought I would add to this one,
Can I get some help proof reading my wiring diagram,
There might be some things that stand out that I should change, Just want to be sure before wiring up the beast!
Last edit: 21 May 2019 23:35 by thefabricator03.
Please Log in or Create an account to join the conversation.
- Grotius
-
- Offline
- Platinum Member
-
Less
More
- Posts: 2419
- Thank you received: 2349
21 May 2019 00:23 - 21 May 2019 00:37 #134417
by Grotius
Replied by Grotius on topic plasma control panel
@Stefan,
Your Pdf is rotated 90 degrees. My neck could not last that long.
Your mese thcad10.... You use a divided arc voltage in from cpc 5 and 6...
I thought for your resolution, mesa is designed for a raw arc voltage? If not why don't you use 0 to 10v input with different jumper settings in HP?
The Metal Box text can be also, " thc module "
I miss the future modbuss port and the future mobbuss connection to the mesa. This one is easy. The python code for the modbuss HP protocoll is provided by the pakastani/india friend at this forum about 2 years ago.
The Estop circuit is a problem. Are you in America?
For The fabricator i give a value of 8 out of 10 for this post. Very, very nice to see this development into the linuxcnc forum.
Nice done !! Very good illustrated. It does me to think about manhatten style. And if that is so, Mesa is learning from you.
Your Pdf is rotated 90 degrees. My neck could not last that long.
Your mese thcad10.... You use a divided arc voltage in from cpc 5 and 6...
I thought for your resolution, mesa is designed for a raw arc voltage? If not why don't you use 0 to 10v input with different jumper settings in HP?
The Metal Box text can be also, " thc module "
I miss the future modbuss port and the future mobbuss connection to the mesa. This one is easy. The python code for the modbuss HP protocoll is provided by the pakastani/india friend at this forum about 2 years ago.
The Estop circuit is a problem. Are you in America?
For The fabricator i give a value of 8 out of 10 for this post. Very, very nice to see this development into the linuxcnc forum.
Nice done !! Very good illustrated. It does me to think about manhatten style. And if that is so, Mesa is learning from you.
Attachments:
Last edit: 21 May 2019 00:37 by Grotius.
The following user(s) said Thank You: thefabricator03
Please Log in or Create an account to join the conversation.
- thefabricator03
-
- Visitor
-
21 May 2019 00:45 #134418
by thefabricator03
Replied by thefabricator03 on topic plasma control panel
Thanks for that,
How do you suggest I wire the E-stop circuit? I am in Australia.
I have read that putting a E-stop between the power supply and the servo drives is a bad idea, Gecko clearly say in there manual that this will damage if not destroy the drive ,
I have also read that putting a disconnect on the AC side of the power supply can damage drives and motors
How do you suggest I wire the E-stop circuit? I am in Australia.
I have read that putting a E-stop between the power supply and the servo drives is a bad idea, Gecko clearly say in there manual that this will damage if not destroy the drive ,
I have also read that putting a disconnect on the AC side of the power supply can damage drives and motors
Please Log in or Create an account to join the conversation.
- Grotius
-
- Offline
- Platinum Member
-
Less
More
- Posts: 2419
- Thank you received: 2349
21 May 2019 01:18 - 21 May 2019 01:30 #134423
by Grotius
Replied by Grotius on topic plasma control panel
@Stefan,
The most safe option is a hard wired (physical wired) E-stop-out function to switch off the main power of the machine.
This above is okey to do in Europe following CE.
If it damages your servo drive, that is not important for court. Court only askes : why is employee damaged? And what are your preqourtions following the spec's in law.
So for Australia, you can contact a local safety institute to take care of the situation.
They will provide you information how to make your machine safe by law. It depend's on machine speed, machine risk class, etc.
For example, a waterjet will provide 4000 bar and is provided with safety line around the machine, because of danger.
Best option is to ask your local safety agent. Most of the advice is for free.
The second way is to use a 2 channel safety channel. This is mostly used by the modern automotive industrie.
forum.linuxcnc.org/24-hal-components/223...?start=710#gallery-3
It's on our forum too. Chimeno, a core member : forum.linuxcnc.org/24-hal-components/223...ver?start=710#133267
For example, if you crash with a tesla, you must wait for tesla experts to make sure for the fire resque peolpe that there is no current around by the car when it's destructed in pieces. If you have a gasoline car, you could be in fire. So how to solve this? It's not solved by one button.
The most safe option is a hard wired (physical wired) E-stop-out function to switch off the main power of the machine.
This above is okey to do in Europe following CE.
If it damages your servo drive, that is not important for court. Court only askes : why is employee damaged? And what are your preqourtions following the spec's in law.
So for Australia, you can contact a local safety institute to take care of the situation.
They will provide you information how to make your machine safe by law. It depend's on machine speed, machine risk class, etc.
For example, a waterjet will provide 4000 bar and is provided with safety line around the machine, because of danger.
Best option is to ask your local safety agent. Most of the advice is for free.
The second way is to use a 2 channel safety channel. This is mostly used by the modern automotive industrie.
forum.linuxcnc.org/24-hal-components/223...?start=710#gallery-3
It's on our forum too. Chimeno, a core member : forum.linuxcnc.org/24-hal-components/223...ver?start=710#133267
For example, if you crash with a tesla, you must wait for tesla experts to make sure for the fire resque peolpe that there is no current around by the car when it's destructed in pieces. If you have a gasoline car, you could be in fire. So how to solve this? It's not solved by one button.
Last edit: 21 May 2019 01:30 by Grotius.