[ Vfdmod ] An easy VFD control over MODBUS RTU
4 years 9 months ago #231875 by s_volenszki
Replied by s_volenszki on topic [ Vfdmod ] An easy VFD control over MODBUS RTU
I just guess, If I give a write command, the VFD echoes back the command what I sent, and do not bother with the CRC calculation (except if it has an error). But when I read data, It must calculate CRC, because the responded data is not related to the request command. I upload the whole SKI-780 RS485 communication protocol documentation, the CRC verification section starts at page 15. If you have time to take a look on it, maybe you can spot on the solution.
I do not know what's next. I try to change Modbus data format and Modbus protocol type, if it will fail too, I think I either start to learn the 0-10V analog solution or the PWM solution (if the VFD supports), or ask may local supplier to give me quotation for a supported VFD (like Omron or Siemens).
Thank you all for your help so far.
The following user(s) said Thank You: COFHAL
4 years 9 months ago #231886 by s_volenszki
Finally I did it :) I made a factory reset on the VFD and started over the settings.
What I did with Sako SKI-780:
  • Set the PP-01 to 01 manual on the VFD control panel (01 = reset factory settings except motor parameters)
  • I used the default 9600 baudrate.
  • Set the command source to RS485 with serial console app (01 06 F0 02 00 02 9A CB).
  • Set the main frequency source to RS485 with serial console app (01 06 F0 03 00 09 8A CC).
  • Changed the Modbus protocol to 31, standard Modbus communication, through RS485 with serial console app (01 06 FD 05 00 1F).
  • Changed the Modbus data format to 8,N,1 (value 3) through RS485 with serial console app (01 06 FD 01 00 03).
What is the most interesting, if I now debug LinuxCNC in terminal, I can see that the CRC Low and high bits are still in reverse order, but works. For example:
Read baudrate
Request: 01 03 FD 00 00 01 B5 A6
Response: 01 03 02 17 75 76 53
Calculated response CRC: 0x5376
Write baudrate
Request: 01 06 FD 00 17 75 76 71
Response: 01 06 FD 00 17 75 76 71
Calculated response CRC: 0x7176
Set spindle speed to 100Hz
Request: 01 06 10 00 09 C4 8A C9
Response: 01 06 10 00 09 C4 8A C9
Calculated response CRC: 0xC98A
So I don't know what was the key parameter for the solution, but now it works, and I hope, next time if someone walks the same way, will end up in less dead ends like me did (I think because of my inattention) :)
4 years 9 months ago - 4 years 9 months ago #231927 by hitchhiker
Replied by hitchhiker on topic [ Vfdmod ] An easy VFD control over MODBUS RTU
hi!
I want to work with your component but i think i am to stupid to do the correct changes to the ini......
i add the ini to this reply and a picture from the registers.
please please please help.... thanks...
Last edit: 4 years 9 months ago by hitchhiker.
4 years 9 months ago #232149 by hitchhiker
hi...nobody has a toip,idea or could help me?!
thanks
4 years 7 months ago - 4 years 7 months ago #236664 by H2B
I've successfully used this to control a Folinn BD600 over MODBUS, and it should also apply to other Folinn (Fuling) models of VFDs. Unfortunately this model requires a reverse command to be sent using a negative percentage to the relative frequency command, which is something I'll try to figure out at a later stage.
Thanks @aekhv for this lovely bit of code!
Hope this information comes in handy for anyone using a Folinn VFD! :D
Here's the ini file I've used on Debian Bullseye with LinuxCNC 2.9 (default release packages work perfectly fine):
[Common] MaxSpeedRPM=24000 MinSpeedRPM=6000 ;AtSpeedThreshold=0.05 [RS485] SlaveAddress=1 SerialDevice=/dev/ttyUSB1 BaudRate=9600 LoopDelay=500 ProtocolDelay=6 ;IsConnectedDelay=10 ConnectionErrorList=110 ConnectionDelay=500 [Control] Address=0x1000 RunForwardValue=0x0001 RunReverseValue=0x0002 FaultResetValue=0x0007 StopValue=0x0006 [SpindleRpmIn] FunctionCode=0x06 Address=0x3000 Multiplier=10000 Divider=24000 [SpindleRpmOut] Address=0x3001 Multiplier=30 Divider=10 [freq-running] FunctionCode=0x03 Address=0x3001 PinType=float PinName=freq-running Divider=10 [bus-voltage] FunctionCode=0x03 Address=0x3002 PinType=float PinName=bus-voltage [output-voltage] FunctionCode=0x03 Address=0x3003 PinType=float PinName=output-voltage [output-current] FunctionCode=0x03 Address=0x3004 PinType=float PinName=output-current Divider=100 [output-torque] FunctionCode=0x03 Address=0x3006 PinType=float PinName=output-torque [run-speed] FunctionCode=0x03 Address=0x3007 PinType=float PinName=run-speed [spindle-load-speed] FunctionCode=0x03 Address=0x300F PinType=float PinName=spindle-load-speed [power-on-time] FunctionCode=0x03 Address=0x301A PinType=float PinName=power-on-time [spindle-run-time] FunctionCode=0x03 Address=0x301B PinType=float PinName=spindle-run-time [fault-code] FunctionCode=0x03 Address=0x8000 PinType=float PinName=fault-code
And here's the files added to the custom.hal to make it work with the interface:
loadusr -W vfdmod bd600.ini --debug net spindle-vel-cmd-rpm => vfdmod.spindle.rpm-in net spindle-at-speed <= vfdmod.spindle.at-speed net spindle-cw => vfdmod.control.run-forward net spindle-ccw => vfdmod.control.run-reverse
Last edit: 4 years 7 months ago by H2B.
4 years 7 months ago #236676 by rodw
Beautiful thanks. I had just about given up on using this with my Folin BD600
I got a feeling my RS485 interface is bad but you have inspired me to keep trying!
It would be helpful if you could outline the changes you made in the VFD settings to enable RS485 control
Time to create page: 0.155 seconds