10 Mar 2020 18:34 #159682
by alkabal
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
The PID and also the limit input is for now fully bypassed until having good result with encoder i use spindle open loop.
Regarding to the encoder.input-index it is possible to invert ?
Really sorry to ask many things but this spindle is for me a real big problem from 2 years ago :
motor shunt burned due to oxydation
burned 2x kbmg + 2x ebay controler
order many Dac/opto board/
Loose a very huge amount of time
Replace 2x wall system with mesa card
Regarding to the capacitor on the power supply port from 7i83, i think is not enough because some time the spindle stop herself without any action...
Thansk a lot, i'm close to cry
Regarding to the encoder.input-index it is possible to invert ?
Really sorry to ask many things but this spindle is for me a real big problem from 2 years ago :
motor shunt burned due to oxydation
burned 2x kbmg + 2x ebay controler
order many Dac/opto board/
Loose a very huge amount of time
Replace 2x wall system with mesa card
Regarding to the capacitor on the power supply port from 7i83, i think is not enough because some time the spindle stop herself without any action...
Thansk a lot, i'm close to cry
Please Log in or Create an account to join the conversation.
- alkabal
- Offline
- Platinum Member
-
Less
More
- Posts: 476
- Thank you received: 52
10 Mar 2020 18:39 #159683
by alkabal
Well you mean increase the 120 ohm resistor ?
halscope with something like 30 rpm is possible but need to test all mode ? (filter/counter/sample-frequency)
the reverted input is not a problem ? (especially for index ?)
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
One change is that you had a 560 Ohm load before and now have a 2000 Ohm load
This may have affected the quadrature symmetry. You may be able to adjust this by lowering the LED current.
Note that you cannot actually see the quadrature signals accurately in halscope unless
you rotate the spindle very slowly
Well you mean increase the 120 ohm resistor ?
halscope with something like 30 rpm is possible but need to test all mode ? (filter/counter/sample-frequency)
the reverted input is not a problem ? (especially for index ?)
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18116
- Thank you received: 5335
10 Mar 2020 18:41 #159684
by PCW
Replied by PCW on topic 7i76e and opto ancoder TCST2103
Yes, you can invert the index, its one of the encoder parameters
It may simply be that running the 7I83 from the KBMG 15V is not practical
Having a "hot"= floating at line voltage analog control is a problematic
It should have worked with an external supply. I suspect your supply was not isolated hence the line power short
It may simply be that running the 7I83 from the KBMG 15V is not practical
Having a "hot"= floating at line voltage analog control is a problematic
It should have worked with an external supply. I suspect your supply was not isolated hence the line power short
Please Log in or Create an account to join the conversation.
- alkabal
- Offline
- Platinum Member
-
Less
More
- Posts: 476
- Thank you received: 52
10 Mar 2020 18:43 #159685
by alkabal
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
Please Log in or Create an account to join the conversation.
- alkabal
- Offline
- Platinum Member
-
Less
More
- Posts: 476
- Thank you received: 52
10 Mar 2020 18:45 #159686
by alkabal
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
For now i don't found at home a supply than work without cutting the house power !
if you have any link you are welcome lol
if you have any link you are welcome lol
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18116
- Thank you received: 5335
10 Mar 2020 19:19 #159690
by PCW
Replied by PCW on topic 7i76e and opto ancoder TCST2103
If you look at the right side of the trace it very close to violating quadrature
you may be able to mechanically adjust this or adjust the symmetry with the
LED current, I suspect a quadrature violation is why you have the 0 velocity spikes.
As far as isolated power supplies go almost any transformer based
wall adapter should work, but should be verified with an Ohmmeter
on the megohm range
you may be able to mechanically adjust this or adjust the symmetry with the
LED current, I suspect a quadrature violation is why you have the 0 velocity spikes.
As far as isolated power supplies go almost any transformer based
wall adapter should work, but should be verified with an Ohmmeter
on the megohm range
Please Log in or Create an account to join the conversation.
- alkabal
- Offline
- Platinum Member
-
Less
More
- Posts: 476
- Thank you received: 52
10 Mar 2020 21:24 - 10 Mar 2020 22:14 #159701
by alkabal
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
Wall adapter isolated found 
Found the parameter
setp [HMOT](CARD0).encoder.00.index-invert 1
trying to sets spindle-index-enable 1, turn the spindle = does not reset the index-enable (sensor is ok checked by multimeter)
I have unconnected encoder B
set to counter mode 1
speed near 30rpm
200 ohm resistor for led
speed near 450 rpm
Found the parameter
setp [HMOT](CARD0).encoder.00.index-invert 1
trying to sets spindle-index-enable 1, turn the spindle = does not reset the index-enable (sensor is ok checked by multimeter)
I have unconnected encoder B
set to counter mode 1
speed near 30rpm
200 ohm resistor for led
speed near 450 rpm
Attachments:
Last edit: 10 Mar 2020 22:14 by alkabal.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18116
- Thank you received: 5335
10 Mar 2020 22:31 #159706
by PCW
Replied by PCW on topic 7i76e and opto ancoder TCST2103
Can you post your hal/ini files? looks like something is really broken there
Please Log in or Create an account to join the conversation.
- alkabal
- Offline
- Platinum Member
-
Less
More
- Posts: 476
- Thank you received: 52
10 Mar 2020 22:34 - 10 Mar 2020 22:52 #159707
by alkabal
Replied by alkabal on topic 7i76e and opto ancoder TCST2103
attached the config 100% from this test
I not remember if i says here that i use rpi4 4gb with buster with information from gnipsel.com tutorial.
Hmm i think about something : my Kill switch is connected to 5v from encoder gnd plugg sharing the same 5v for encoder (second wire from kill switchconnected to input 0)
Gnd from optocoupler encoder connected to encoder gnd plugg
I not remember if i says here that i use rpi4 4gb with buster with information from gnipsel.com tutorial.
Hmm i think about something : my Kill switch is connected to 5v from encoder gnd plugg sharing the same 5v for encoder (second wire from kill switchconnected to input 0)
Gnd from optocoupler encoder connected to encoder gnd plugg
Last edit: 10 Mar 2020 22:52 by alkabal.
Please Log in or Create an account to join the conversation.
- PCW
-
- Offline
- Moderator
-
Less
More
- Posts: 18116
- Thank you received: 5335
10 Mar 2020 22:52 #159708
by PCW
Replied by PCW on topic 7i76e and opto ancoder TCST2103
Can you look at the encoder velocity pin to eliminate other possible problems
also, if you have a 1 KHz servo thread you should use 1 KHz for Halscope
so you dont miss things
also, if you have a 1 KHz servo thread you should use 1 KHz for Halscope
so you dont miss things