Emergency STOP on mesa card 7i76e

More
15 Jul 2021 23:31 #214946 by sibelius
Good evening everyone,

I was thinking to add an Emergency button to my machine.
I would like that when I press the button my card does not power off and the intention is to stop only the motion and the spindle and this is exactly what happen when I touch one of my limit switch.
Saying so my first thought is to wire the Emergency button in parallel with one of the limit switch.

I would like to hear some advice from the experts.

Thank you very much in advance for any comments.

Regards,
V.
 

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 01:01 #214968 by scotth
It is best that an Emergency Stop not run through logic. You can add it into the logic, but it is best to kill the power to the drives directly by disabling a relay.

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 02:10 #214980 by sibelius
Hi, thanks for your answer
If I correctly understand what you are saying, what you are suggesting is to cut of power from the step motor driver.
If I interrupt the current to the drive there is not the chance to loose step in doing this?
I am thinking to restore job after emergency occurs so keeping steps is a key point.
Why you are saying that is best not to add emergency button to logic?
Thanks again.

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 04:18 #214989 by scotth
E-Stop is just that. It is to stop the machine and stop damage to you or the machine.
Single block and feed rate override are used to stop a program during operation. You won't care about loosing a step to avoid a wreck or your hand. You can always rehome or set zero, your safety is far more important. If you have enough digits to count to ten when you start a job, the main goal is being able to do that at the end of the day also.
The following user(s) said Thank You: phillc54, rodw, sibelius

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 08:09 #215001 by sibelius
That's pretty good reason ! Inside me I knew the answer but I need some reminding to opt for your suggestion. Now I have to look around for some wiring diagram and hal implement code.

Thanks again.

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 08:23 - 16 Jul 2021 08:24 #215002 by itsme
Depending on your machine i would not just cut the power of the driver.
The axes might move free afterwards, z axis might fall down.
I cut enable and steps with safety relais so motors stop. Also spindle is diabled and Power cut after 10 seconds with safety time relais.
Last edit: 16 Jul 2021 08:24 by itsme.
The following user(s) said Thank You: sibelius

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 08:51 #215005 by rodw
most estop buttons (well the ones I bought anyway) have two contacts. One is normally closed and the other is normally open.
Wire the mains power to your motors through the NC side and wire field power through the NO side. So when you push the button it cuts the mains power and lights up a Mesa input to tell Linuxcnc estop has been pressed.

This becomes a compliant system. You should not use relays in a safety circuit unless it is a standards approved  safety relay. The one I purchased cost me AUD $250 plus another $50 or so for the contactor which is required by the relay. Same story though. Drop power to the motors and signal to Linuxcnc that estop has been pressed...
 
The following user(s) said Thank You: sibelius

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 09:50 #215012 by sibelius
thanks for your help

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 09:52 #215014 by sibelius
Thanks Mr Rod.
My emergency stop button is like that one you indicated, I have to do a bit of thinking about wiring and updating my hal file.
much appreciated your help
The following user(s) said Thank You: rodw

Please Log in or Create an account to join the conversation.

More
16 Jul 2021 10:06 #215016 by bevins
Well, my opinion is safety relays are overrated. They are just inputs and relays and microprocessors that is certified to work? Really?
I don't buy it, you can do the exact same thing with relay and inputs with mesa board. ITs electronics and whether it is in a certified safety relay or hard wired relay circuit, it will drop out relays when power is removed. I don't know about you but I have worked on many machines built from scratch and retrofits and I have never had a relay fail or an estop circuit fail. I have replaced a Siemens safety relay though on a Morbideli P2P router.
I see alot of the safety relays in large routers when retrofitting and I use them. I wouldn't pay for them if I had to buy them cause you can create the same  circuit with relays, timers etc...... Especially with the hobby machines 2'X4' and want to remove power from the drives on estop circuit and put safety relays in. A bit overkill don't you think? 

I can see maybe the need if you have a 10 foot 10,000 lbs router with a gantry that weighs 1500lbs moving at 700ipm, Mine I used the existing safety relay because it was there but it doesn't do anything magical, at least nothing you cant do with some relays etc...

Just my 2 cents and sorry for the rant,
The following user(s) said Thank You: sibelius