phillc54 wrote: Wow, that is a mean spike you get 100mS after torch on for the second cut.
So there a maybe a few different ways around this.
- install a current sensor in the torch lead and use that for an Arc OK signal
- I could add a Arc OK on delay so the arc voltage needs to be within limits for nnn amount of time before Arc OK is true
- I could add a Arc OK off delay so the arc voltage needs to be outside limits for nnn amount of time before Arc OK is false
- I could add a Arc OK High inhibit so Arc OK won't go false if the arc voltage is too high
Please Log in or Create an account to join the conversation.
phillc54 wrote: Wow, that is a mean spike you get 100mS after torch on for the second cut.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
PCW wrote: Sounds like if it not already done, simply masking the high voltage test for
a settable period of time after the torch on command would fix the issue.
Also just setting the high threshold to a bit under the open circuit voltage
when waiting for arc OK seems like it would also fix the issue